Hello Brian,

Let’s start with the easy question first, the order of stacking lugs on a 
single stud. The equipment’s protective earthing conductor should go on the 
bottom and have a lock washer and nut on top of it before any other bonding 
conductors are added. The rationale is that you don’t want service personnel to 
have to remove the main earthing lug to remove any other parts. If the main 
earthing lug is bolted below other lugs, there is a lower risk of it being 
disturbed in any servicing procedure. There is one advantage of placing a lock 
washer and nut over each additional lug added. If two lugs are under the same 
nut, there is a chance that they could rotate against each other loosening the 
nut above them and compromising the connection. I recommend a separate bonding 
stud for each lug if the equipment is expected to require servicing that 
removes bonding conductors to remove parts.

If you have a welded, press fit or similarly fixed stud, you likely do not need 
to mask of the paint or coating around the stud. The flat faces of the nuts 
will make good electrical contact with the grounding lugs and the threads of 
the nut will have good electrical contact with the stud. However, I have had at 
least one NRTL tell me that they wanted the paint masked off in a ring around 
the stud. That NRTL was in the minority. I’ve had differing opinions on whether 
split or star-tooth lock washers are better at cutting through paint, coatings 
or oxidation. I take no position on that, and it shouldn’t matter based on a 
connection through the threads.

Bolts and screws pose a different problem. These may not make as good of 
electrical connection to the chassis. Lock washers that cut through coatings 
and oxidation will likely be required. That being said, I have a personal 
aversion to bolts and screws for bonding. The exception is where there is a 
threaded insert or otherwise set of well formed threads in the chassis where 
the bolt will make a good connection through the threads. Screws are too easy 
to strip out if overtightened, thereby compromising the bonding.

I’m sure these rules are written down somewhere, but I don’t know where that 
would be. I would be interested in knowing, because I assume there are written 
rules somewhere that would tell me that everything I just wrote is wrong.

Ted Eckert
Microsoft
The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: Brian Kunde <bkundew...@gmail.com>
Sent: Friday, June 7, 2019 6:10 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Stacking Grounds on a Stud


My question(s) is about stacking ground lugs on a single stud for the 
Protective Earth Terminal inside of a piece of electrical equipment (IT or Lab 
Equipment).

Where is it documented how to properly stack ground lungs?


I have seen this done several ways:

1. A welded stud or just a bolt (#6 or #8 machine screw) pushed through a hole, 
 with the Power Cord Ground Conductor lug stacked FIRST, followed by additional 
lugs. I have seen this with and without locking washers between the lugs.
2. I have seen the above with Nuts or Locking Nuts between each Lug.  This 
method seems much more reliable to me but the nuts take up a lot more space 
limiting the number of lugs that can be stacked.

3. I have seen the above on black oxide, anodized aluminum, or powder coated 
painted metal with not attempt to scrape off the non-conductive material to 
ensure a good bond.



I just evaluated a 3rd party product that had a #6 machine screw pushed through 
a hole in a powder coat painted metal plate with 7 ground lugs and one nut 
holding it all together.  With very little effort, the nut became loose and the 
ground became intermittent.  Yet, this unit has passed an NRTL inspection.


It is my understanding that PE Ground bonds made with a Screws cannot be 
stacked.  One Lug, One Screw.  Is this documented somewhere?

Thanks much for any input.

The Other Brian.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C7469dd0e67544791dcbf08d6eb498a4e%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636955098431716738&sdata=n4c916AcSp4EW0Q4Zsq17%2BkJSWxNWMkAnERA%2BBKOewk%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C7469dd0e67544791dcbf08d6eb498a4e%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636955098431726733&sdata=DqklhK1LuhkxhiDkk5z%2F8sMuYxQYzNKgleZrmuO1Bp0%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C7469dd0e67544791dcbf08d6eb498a4e%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636955098431726733&sdata=sVe0wqtr1L3%2F2cmXhBs59uSQ7Yfvh%2FiHibRn47UseBQ%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C7469dd0e67544791dcbf08d6eb498a4e%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636955098431736728&sdata=lFYZNuWzEix0GelFeMpo5aLGqUJ7ojh6zkOXpc5UW%2Fw%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C7469dd0e67544791dcbf08d6eb498a4e%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636955098431736728&sdata=WQYclTGpzuamL0AsBdOpTWVX7sdCoZgopv9q1VItWkk%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to