The rationale I remember learning is that the main grounding/earthing 
connection must be made in a way such that any repairs would not need to 
disconnect that main grounding connection. Let me use Mr. Woodgate’s examples.

If you have an insulating terminal block, replacing the terminal block could 
disrupt the grounding connection. If the repair person fails to connect the 
ground on the load side, the device will likely still function, but it will 
have lost its safety ground. If you connect incoming ground to the chassis 
first, and then to the terminal block, replacing the terminal block would not 
disrupt the grounding connection even if the wiring on the terminal block is 
connected incorrectly.

However, if you have a grounding terminal block, where the ground connection in 
the block is a direct metal connection to the chassis, replacing the terminal 
block would reconnect the incoming ground to the chassis. Of course the ground 
wring to the terminal block could be done incorrectly, but you have at least 
removed some of the risk of a missing grounding connection. When using 
appliance couplers, filtered couplers can serve multiple purposes. They can not 
only provide EMC filtering, they make a direct bond between incoming ground and 
the chassis. This would serve a similar safety purpose as a grounding terminal 
block.

Of course, for cord connected equipment, there is the repair of replacing the 
cord that requires disconnecting the ground wire. All we can do is to make the 
design fool-resistant. Nothing can be foolproof in this world of talented fools.

Best regards,
Ted Eckert
Microsoft Corporation

The opinions experessed are my own and do not necessarily reflect those of my 
employer.

From: Bill Owsley <[email protected]>
Sent: Monday, September 23, 2019 9:45 PM
To: [email protected]
Subject: Re: [PSES] Grounding of metal cabinet

Our safety regulators have insisted that power cord safety ground/earth go 
first to the metal chassis, with rare exceptions.  Exception, the majority of 
chassis is plastic, with internal metal structures to tie it all together.
Only the screw heads are exposed and tied to some of the internal metal chassis.
A complex system of wires, washers, terminals, etc. were needed to ensure it 
was all one complex earth grounded structure.

I AM NOT a safety engineer, but I do know a few !
- Bill





On Monday, September 23, 2019, 07:42:11 PM EDT, Pete Perkins 
<[email protected]<mailto:[email protected]>>
 wrote:



               This is a great discussion.  It took some work to get most of 
the world to use a solid, direct earth/ground connection in cabinets and 
equipment.  CSA published detailed connection diagrams and pushed direct 
connection into many product standards with good results.  The struggle has 
been since the modularization of components and units has come into play.  This 
raises questions as to how to interconnect everything together in a way  that 
preserves the integrity of the earthing/grounding connection when it is a 
principle safeguard against electric shock.  As an OF (= Old Fellow, in polite 
company) I prefer that the earth/ground wire be tied to the mechanical 
structure of the cabinet or equipment first then carried to the distribution 
components.  It is very difficult to destroy the integrity of this earthing 
first philosophy.  There are many scenarios where the quick install/quick 
connect terminal block can be disconnected from the earthed rail and leave the 
cabinet/equipment without the needed earthing/grounding connection.  Let’s keep 
the focus on providing the highest integrity protection scheme in place (and 
common practice).



:>)     br,      Pete



Peter E Perkins, PE

Principal Product Safety & Regulatory Affairs Consultant

PO Box 1067

Albany, Ore  97321-0413



503/452-1201



IEEE Life Fellow

[email protected]<mailto:[email protected]>



Entropy ain’t what it used to be



From: John Woodgate <[email protected]<mailto:[email protected]>>
Sent: Monday, September 23, 2019 4:19 AM
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] Grounding of metal cabinet



The question is how the cabinet is earthed if the PE wire goes to a terminal 
block. If  a wire comes out of the terminal block to a stud on the cabinet, 
that is less reliable than a solid connection.  I suggest you take the advice. 
It doesn't apply if the 'terminal block' is  not an insulating block with metal 
inserts but a metal block firmly attached to the cabinet.

Best wishes

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates 
www.woodjohn.uk<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.woodjohn.uk&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245765905&sdata=spnE6aXfHr7UAFO31TVLojkdhSSuidZEmmVEemhnn2s%3D&reserved=0>

Rayleigh, Essex UK

On 2019-09-23 11:33, Amund Westin wrote:

A flexible 1-phase AC cable is entering a metal cabinet and the PE-wire is 
directly connected to an Earth terminal block (green/yellow).

Some years ago, a safety engineer told me that the earth wire should first be 
connected to a ground stud inside the cabinet via a lug terminal climp and 
fastened with a nut. From the stud, a green/yellow wire should connect to the 
Earth terminal block.



I thought it’s OK to go directly to the Earth terminal block, right? …



BR
Amund Westin







-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245775898&sdata=qyw4BaoD9mvegc3Ro8kPotkE6whqaL9UN2pSwsJppDo%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245775898&sdata=Ux8sCWpBbqqc09Cb2mlrkJZcTovCPuvLsGjEPCTQpuY%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245785893&sdata=Pw1csDxEZZoNbn3TUVbA%2BAmM4tM4WOmBDZ6t32dvU0o%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245785893&sdata=ti0x9Bs2N%2F0krGT%2BnrGIU%2BBWP5TKHqqStXPB2uJMsfo%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245795886&sdata=9fy0ndB75h1KfcNI8IBkMGF2DNfT%2Ftlp6DO%2FRgOikwk%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245795886&sdata=Ll1d%2FoUp90d83ktsIESwwoaZpTgwLDXxpF7nEGsmVuQ%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245805882&sdata=kU4bGUPLn704q29B4kTAug27tiTOsZgaEHREBzFlLXg%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245805882&sdata=EBePtxOZ3Y21CavWFFIHMevC8AZOOCr3wtbqm2i8dpM%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245805882&sdata=rt7PnIRb7LtjdIFla%2FCegSxAaJ2aE2oOuWdQltZjgEs%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245815875&sdata=2NPJba5F0ZGaFqjgBxjYazko7CwGacennJZ4Px0XZN0%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245815875&sdata=HyZu3u5dXyWekggqINcokArUkjDbQ3IBeHDU904nOpA%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245825869&sdata=8pZWpeJwHGJdl%2FLD8fmN6bjI0b6pejON6eU3bVVWt%2Bg%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245825869&sdata=KwbN0hp14KImTs8iBmVjLJlthshvWJQy%2B%2B5F9t49nWA%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245835863&sdata=X%2B9O3xt5ACBk86f%2B%2FQyDfLGsjjL4bNLoTbds5mNxVfI%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245835863&sdata=JwparycL54%2FlJSmNNdmwdwIVm2Guk3yi%2FD2XKFBaxuA%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245845856&sdata=wHRwNlnU4ojlDrF65NbOG7pMZzgNa8x%2BdjzwJvp4hyY%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245845856&sdata=zKCmdLr%2FUcH63V3T9ZTnej4oQ69y3JwL7yyh60uKO8E%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245855850&sdata=ntwsLBn9dCo0IHQNrXn8uTfAQ2jYciLdDNMJbA4jTT0%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245855850&sdata=pWVvDq8GNVlbWhpSWlpbHyzKhDhra5x6LwCPfsFR1%2B4%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://nam06.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cc5d624bb977847beec2408d740ab67fd%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C637048977245855850&sdata=mMrzR88KKBiqKLOHP77V5bNjjJSBiQgZAr%2FJr2nDMgw%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to