Rich & Pete. Thanks for your excellent explanation to this topic. Good
lesson. Much appreciated.
I can only speak for myself but I strongly believe that this
topic/understanding needs to be brought more into the spotlight based on my
previous discussions with some of my peers.
Any of you care to do a whitepaper on this?

Regan

On Wed, Feb 26, 2020 at 7:43 AM Pete Perkins <[email protected]> wrote:

> Regan et al,
>
>
>
>                The basic electric shock info for the levels selected in
> the product standards come from IEC 60479 series, Effects of electric shock
> on the human body…  There are two sets of curves in IEC 60479-1 based upon
> the data collected and evaluated (from the literature).  One set of curves
> is for AC and the other is for DC.  These plot three body effects;
> startle-reaction, letgo-immobilization and Ventricular Fibrillation as a
> function of time.  The names for these effects primarily come from the
> effect of AC currents on the body.  The DC effects are not as well defined
> physiologically but are given the same names for consistency.  The product
> committees end up picking levels which seem appropriate for the application
> and the values are not fully consistent between product standards, in spite
> of the work of the IEC to make it so.
>
>                A major difficulty is that the body effects are from the
> current while the product committees would like to specify voltage, which
> is easier to measure and verify compliance.
>
> The IEC long ago issued a simple 1201 Voltage Limits standard, aka 61201,
> which was updated using a more complete evaluation and had a myriad of
> curves for the various conditions based upon the choice of contact
> parameters selected.  This is so much more complicated than just selecting
> a fixed voltage for most conditions and is not generally used in product
> standards.
>
>                So, in short, whether one picks 60Vdc or 70Vdc is not very
> relevant in the overall human body effect picture; nor is a change of 4Vdc
> around any of these values.
>
>                Finally, as Rich stated, the DC value is not related to the
> AC value by the sqrt 2.  This works well for moving from AC to equivalent
> DC voltage for hi-pot testing purposes but provides no path to the human
> body effect which is different, as has been discussed here.
>
>
>
> :>)     br,      Pete
>
>
>
> Peter E Perkins, PE
>
> Principal Product Safety & Regulatory Affairs Consultant
>
> PO Box 1067
>
> Albany, ORe  97321-0413
>
>
>
> 503/452-1201
>
>
>
> IEEE Life Fellow
>
> IEEE PSES 2020 Distinguished Lecturer
>
> [email protected]
>
>
>
> *From:* Regan Arndt <[email protected]>
> *Sent:* Tuesday, February 25, 2020 8:49 PM
> *To:* [email protected]
> *Subject:* Re: [PSES] IEC 61010-1:2010 hazardous DC voltage
>
>
>
> Hi Rich.
>
> Thanks for your feedback.
>
>
>
> Correction/clarification. I was not trying to ‘convert’ to DC using 1.414
> (root 2).
>
> I merely used that ‘multiplication factor’ (1.414 & sometimes just 1.4)
> based on the widely used/misused?/abused? that is used in the industry when
> determining ‘equivalent’ DC values, just like one commonly does when
> calculating the hipot test values.
>
>
>
> See:
> https://electrical-engineering-portal.com/what-is-hipot-testing-dielectric-strength-test
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__electrical-2Dengineering-2Dportal.com_what-2Dis-2Dhipot-2Dtesting-2Ddielectric-2Dstrength-2Dtest&d=DwMFaQ&c=q6k2DsTcEGCcCb_WtVSz6hhIl8hvYssy7sH8ZwfbbKU&r=9-kTQUJB47k5_bHz_YekCwOWfoQDGgqgofVdnvpCXhM&m=X4OfXcJKn2LCMhQAhagkIEb6yDHp7Th9Mn0aSM9F6M4&s=57RvY_cM21TMTgAGuiIGMnZD0a7EcjWCvdfn0geu-kw&e=>,
> where Jignesh Parmar quotes in his article: “Therefore, if we use dc test
> voltage, we ensure that the dc *test voltage is under root 2 (or 1.414)
> times the ac test voltage, so the value of the dc voltage is equal to the
> ac voltage peaks.”*
>
>
>
> Another classic example comes from the 60950 standard for hipot values.
> 1500 VAC/2121 DC (calculation factor = 1.414)
>
>
>
> That being said, I look forward to hear a response from someone on TC66 on
> why they chose 70V.
>
>
>
> It would also be great if you could do a whitepaper (& speak) on the
> understanding of how the body reacts to AC & DC for this year’s PSES
> symposium in Chicago? 😉
>
>
>
> Regan
>
>
>
> On Tue, Feb 25, 2020 at 4:07 PM Richard Nute <[email protected]> wrote:
>
>
>
>
>
> Hi Regan:
>
>
>
> The “bump” occurred from 1st edition, 1990, to 2nd edition, 2001.  The 2nd,
> 2001, and 3rd, 2010, are the same.
>
>
>
> Be careful with your math and DC interpretation.  The rms voltage limit is
> 33.  The ac peak is 1.414 x 33 = 46.7.  The DC is 70, which is unrelated to
> the AC voltages (which is because of how the body reacts to AC and DC).
>
>
>
> As to the rationale for the change from 1st to 2nd, I suggest you find a
> member of TC66 and ask for the documents preceding the 2nd.
>
>
>
> Touch voltages are specified in IEC TS 61201.  In this standard both 30
> and 33 volts rms are listed, with very little difference in body reaction.
> Same for 60 versus 70 volts DC.
>
>
>
> Best regards,
>
> Rich
>
>
>
>
>
>
>
> *From:* Regan Arndt <[email protected]>
> *Sent:* Tuesday, February 25, 2020 2:38 PM
> *To:* [email protected]
> *Subject:* [PSES] IEC 61010-1:2010 hazardous DC voltage
>
>
>
> Dear fellow members,
>
>
>
> I am trying to understand the 'rationale/history' of why TC66 bumped up
> the DC voltage by a mere 4 volts for hazardous voltages.
>
> As we know by simple math, 46.7 Vp x 1.414 = 66 VDC.............where, why
> and how did the extra 4 volts come about?
>
> I need a history lesson here.... ;)
>
>
>
> Also, will these voltages also come back to normal in Ed 4? (i.e. 42.4 Vp,
> 60 VDC)
>
>
>
> Thanks for shedding any light on this?
>
>
>
> Regan Arndt
>
>
>
>
>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to <
> [email protected]>
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) <http://www.ieee-pses.org/list.html>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell <[email protected]>
>
> For policy questions, send mail to:
> Jim Bacher <[email protected]>
> David Heald <[email protected]>
>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to <
> [email protected]>
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) <http://www.ieee-pses.org/list.html>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell <[email protected]>
>
> For policy questions, send mail to:
> Jim Bacher <[email protected]>
> David Heald <[email protected]>
>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to