Lauren & Brian,                

 

Be careful with considering a test.  The source must have a SSCurrent equal to 
(or greater than) the largest SCCR component (sounds like the 200kA fuse from 
your description).  This level of available current is not found in your usual 
lab setup.  

 

I have seen disastrous test results when the entire system is properly tested 
even tho it was claimed to be sufficient because of an earlier test at a lower 
SSCR setup.  

 

:>)     br,      Pete

 

Peter E Perkins, PE

Principal Product Safety & Regulatory Affairs Consultant

PO Box 1067

Albany, ORe  97321-0413

 

503/452-1201

 

IEEE Life Fellow

IEEE PSES 2020 Distinguished Lecturer

 <mailto:[email protected]> [email protected]

 

Entropy ain’t what it used to be

 

From: [email protected] <[email protected]> 
Sent: Friday, October 30, 2020 9:36 AM
To: [email protected]
Subject: Re: [PSES] Short Circuit Current Rating (SCCR)

 

Hi Brian, 

 

UL 508A Supplement SB has a method for this. Also the www.semi.org 
<http://www.semi.org>  standard SEMI S22 has a method in one of it’s ‘Related 
Information’ sections. The SEMI standard RI section includes a reprint of an 
SCCR  guide from Bussmann. The link S22 provides no longer works (it looks like 
bussmann was acquired by Cooper was acquired by Eaton since then), but it looks 
like Eaton has some useful guidance in a big guide they have for electrical 
protection in general (probably with a generous dose of Eaton products) at 
http://www.cooperindustries.com/content/dam/public/bussmann/Electrical/Resources/technical-literature/bus-ele-an-3002-spd.pdf

 

Best Regards, 

-Lauren

 

From: Brian Kunde <[email protected] <mailto:[email protected]> > 
Sent: Friday, October 30, 2020 8:55 AM
To: [email protected] <mailto:[email protected]> 
Subject: [PSES] Short Circuit Current Rating (SCCR)

 

Greetings to all. I hope this finds you well.

 

Once again the subject of SCCR has come up.  I have struggled for years to find 
a document or someone who can explain this to me.  The bottom line is I need to 
know how I would determine the SCCR for my product.  In one case in particular 
I am currently working on, it is a 3 phase motor-driven industrial device. It 
draws less than 8 amps at 230V. Internal to the device, we have three "CC" type 
fuses with a SCCR of 200KA.  However, ahead of that we have a lockout/tagout 
disconnect device that is only rated 10KA SCCR.  

 

How exactly can I determine the SCCR of my device?

 

Thank you all.  

 

The Other Brian

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected] <mailto:[email protected]> >

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) 
<http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]> >
Mike Cantwell <[email protected] <mailto:[email protected]> > 

For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]> >
David Heald <[email protected] <mailto:[email protected]> > 

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected] <mailto:[email protected]> >

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) 
<http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]> >
Mike Cantwell <[email protected] <mailto:[email protected]> > 

For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]> >
David Heald <[email protected] <mailto:[email protected]> > 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to