Hi Brian:
“Touch current” is current through the body when it touches two conductors. By
convention, touch current is measured through a 2,000-ohm resistor in series
with the PE conductor. Touch current only exists if two conductors are
touched, for example, when the PE is open. If the current is sufficient, it
can cause enough L-N imbalance current to trip the GFCI.
PE current is measured with an ammeter in series with the PE conductor. In
your situation, PE current, not touch current, trips the GFCI (because the PE
is not open).
An isolation transformer on the load side of a GFCI will provide a return
current path to the isolation transformer rather than an imbalance of current
through the GFCI. (I am assuming the isolation transformer neutral is
connected to ground). The GFCI will not see an imbalance between L and N.
Best regards,
Rich
From: Brian Kunde <bkundew...@gmail.com>
Sent: Monday, August 29, 2022 5:45 AM
To: ri...@ieee.org
Cc: EMC-PSTC@listserv.ieee.org
Subject: Re: [PSES] High Touch Current and GFCIs
If I have EE or a rake of equipment or several pieces of equipment plugged into
a power strip that has a combined touch current that trips a GFCI, what can be
done about that? Will an isolation transformer solve the problem?
Thanks,
The Other Brian
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org>
For policy questions, send mail to:
Jim Bacher: <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1