Hi Steve:
Mains circuits are subject to lightning and switching transients both
line-to-neutral and line/neutral-to-ground. The transients are normal; to
prevent insulation breakdown and consequential electric shock, the electric
strength of mains-to-ground and mains-to-other circuits insulations must exceed
the expected transient voltages. (Electric strength requirements based on
transient voltages are specified in IEC 60664-1, supported by research by
Stimper.)
The mains transients can be capacitively coupled to secondary circuits,
depending on the configuration of the isolation scheme. In most cases, the
isolation scheme and the impedance of the secondary circuit attenuates the
transient voltage to near zero. This point seems to be recognized by IEC
60101-1.
Then, as Brian Kunde has said, secondary circuit devices such as relays,
solenoids, and switching can generate transients in the secondary circuits. In
most cases, such transient voltages are small and are attenuated by the
secondary source impedance.
IEC 60601-1 has a similar requirement, although it includes clearance
requirements for no-transient secondary circuits. IEC 62368-1 does not have
such a requirement. I wonder what evidence or research supports transient
voltages in secondary circuits?
Best wishes for the holiday season,
Rich
From: Steve Brody <sgbr...@comcast.net>
Sent: Thursday, December 1, 2022 12:51 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Secondary creepage/clearance
I have a client who has a secondary pwb that has traces and vias that may have
100 vdc on them adjacent to ground.
Per 61010-1 there is a requirement for spacing and/or dielectric test, both
depending on what the mains voltage is.
The question is why is the mains voltage a consideration or concern if the
100vdc secondary voltage is several layers of impedance and circuitry from the
mains?
Is it a concern that a surge on the mains would trickle down to the secondary
circuit, or is there another reason/rationale?
I suggested that a dielectric test per Table 6 [in A1] would suffice and put
the issue to rest for this product, but the question from the designers remains
as to why is it a concern in the standard of what the mains voltage is.
Is there anything in the standard, that I haven't found, that does not require
Table 6 to be followed if there is no way for a mains surge to impact the
secondary voltage?
I look to the experts for an explanation.
Thanks,
Steve Brody
<mailto:sgbr...@comcast.net> sgbr...@comcast.net
C - 603 617 9116
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> >
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> >
_____
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org>
For policy questions, send mail to:
Jim Bacher: <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1