I think you have a good handle on E-stopping. Now you need to address how
you get out of E-stop. Once you hit a limit switch, all the power is shut
down. How do you get the machine off the limit switch without power? Does
your machine have hand cranks? I assume that you have separate home switches
to home the machine (some of us use the limit switches to do that).


Personally, I don't like the idea of the limit switches in series. I would
like the computer to know which limit was hit. So, if the X+ limit is hit,
the computer could allow motion in the X- direction to get off the X+ limit
switch. One might argue that *soft* limits are supposed to handle that case.
Or, you could have each of the limit switches have it's own relay. (Or be a
muli pole switch.) Then the limit switches could be in series AND the
computer could tell which limit had been hit. A separate limit override
could then short across the series chain of limit switches to close the
chain while the computer jogged off of the limit. That limit override might
even be a manual press switch that had to be held while the jog took place.

I guess there are really two e-stop cases. Case 1 is the bug in the g-code
case where there is a need to hit the big red button. That might be fairly
frequent. Case 2 is the hardware/software case where the machine "went
crazy" and ran through the soft limits. That should NEVER happen.

Case 1 should be easy to recover from. Case 2 does not have to be easy to
recover from.

Sorry I've rambled. If you have the answer to getting out of e-stop, you're
all set.

Ken



[EMAIL PROTECTED]
Mark Kenny Products Company, LLC
55 Main Street                     Voice: (203)426-7166
Newtown, CT 06470                    Fax: (203)426-9138
http://www.MarkKenny.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Anders
Wallin
Sent: Friday, December 15, 2006 4:55 PM
To: Enhanced Machine Controller (EMC)
Subject: [Emc-users] E-stop circuit ?


Hi all, could I have some comments on the following E-stop circuit idea.
The core idea emerging from thinking about this is to wire dangerous
things in series(wire OR) and use the end result of this in
parallel(wire AND). That way the E-stop chain is cut if device1 OR
device2 OR device 3... fails, and the resulting signal stops EMC AND
cuts power to VFD AND cuts power to servo drives AND ...

Here is what I have come up with:

start at the HAL pin E-stop-out. It will be high whenever EMC thinks
it's OK to go out of E-stop.

E-stop-out drives the coil of a NO(normally open) relay. This relay
connects +12 V to the beginning of the E-stop chain only if E-stop-out
is high.

On the +12V wire, a number of NC(normally closed) switches follow: Red
E-stop buttons (2), Limit switches(6), NC relays on the servo amps(3).

At the end of the chain we are going to have either +12V if everything
is OK, or 0V if we are in E-stop.

Use the +12V to power the coils of three NO relays (coils in parallel):
1. one relay connects +5V to E-stop-in telling EMC everything is OK
2. one relay grounds the Poweron/ input of a Pico Systems power switch -
that will give power to the servo drives.
3. one relay connects 230 VAC power to a VFD which powers the spindle motor

If the E-stop chain breaks for any reason all of the relays will go to
their NO state making E-stop-in go low, cutting power to servo drives,
and cutting power to the VFD.

If this sounds confusing there's a picture at
http://www.anderswallin.net/temp/e-stop.png
which might help... (the E-stop chain is the blue line, the VFD relay
would obviously be two-pole, a transistor driving relay1 is needed)


Some questions I have:
-wiring three relays in parallel at the end of the chain will result in
three times the current needed to pull one coil of the relays. Is this
going to be a problem ? (other than that the +12V supply must cope)
-is it a good idea to just cut the AC power to the VFD in an E-stop
situation ? are there any other better ways to safely stop the spindle ?
-should I also hardwire the servo drive amp-enable signals so that they
go low on E-stop?
-If I connect the common terminal of the limit switches to the
'upstream' end of the E-stop chain, can I wire the unused NO output of
the limit switch to another HAL pin ? This way an E-stop due to a limit
switch could be diagnosed by EMC as coming from a specific limit (+/-)
and axis (XYZ).


thanks for any comments,

Anders

-------------------------------------------------------------------------
Take Surveys. Earn Cash. Influence the Future of IT
Join SourceForge.net's Techsay panel and you'll get the chance to share your
opinions on IT & business topics through brief surveys - and earn cash
http://www.techsay.com/default.php?page=join.php&p=sourceforge&CID=DEVDEV
_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

-------------------------------------------------------------------------
Take Surveys. Earn Cash. Influence the Future of IT
Join SourceForge.net's Techsay panel and you'll get the chance to share your