Hmmm.

Interesting idea to just have coils and registers presented as pins.  
Then you'd only need to specify how many of each you want to access, 
along with the base address.  It gets more complicated if you need to 
allow access to registers/coils in multiple discontiguous ranges.

There's also a problem with multi-register values.  Some devices can 
handle 32-bit values, which are generally composed of two 16-bit %Rxx 
values.  I'm not sure if the spec tells you to use a certain 
endian-ness, so it may be necessary to be able to specify that as well.  
This is why I was thinking about a higher level spec for specific 
devices (ideally with a low-level core that's at least from common 
source code, and at best a single shared module).  It would be much more 
readable in HAL to have a modbus.0.vfd.0.spindle-speed pin rather than 
having something like the inverse of a scale block to convert from float 
to whatever integer units the VFD uses, then possibly to split that into 
two 16-bit words for connection to modbus.1.register001 and 
modbus.1.register002.  It would also be possible now that I think of it, 
to have a VFD module that converts from "engineering units" to whatever 
registers and coils the modbus interface provides.  The downside is that 
you end up with a lot of HAL connections that aren't really useful, and 
can cause major problems if they're screwed up (imagine the oops of 
swapping the high and low words of a spindle speed, for example).

The communications parameters you mentioned look as though you have in 
mind only a single device per serial port.  I think what you need here 
is a port specification per serial port (baud/parity ...), and a "port + 
address" spec for each device.  Since modbus can handle multiple devices 
per serial port, it would make sense to have that capability in the driver.

I should stop thinking about it, because it keeps getting more complex 
the more I do  :)

- Steve

Kirk Wallace wrote:

>Below is a beginning of a first pass at writing an EMC Modbus RTU
>interface spec. Any comments are welcome.
>
>"
>EMC should talk to Modbus RTU devices through a Modbus RTU component.
>Each device, hence Modbus address, would have a Modbus component
>instance, modbus-rtu.0, modbus-rtu.1, etc. For example, a spindle or
>tool change signal might have an HAL link of "net motion.spindle-on
>modbus.0.coil001" and "net iocontrol.0.tool-change modbus.1.coil003". If
>a device meets modbus standards, no device dependant driver would be
>needed. Each modbus instance would need parameters set for; serial port
>number, address number, baud rate, parity, number of stop bits, latency
>time, response time-out, etc., to match the characteristics of the
>device being attached.
>"
>

-------------------------------------------------------------------------
This SF.net email is sponsored by: Microsoft