Howard Chan wrote: To be perfectly honest, I can't understand your words. But scope traces are easier to translate, so let's look at your picture:
> http://myweb.polyu.edu.hk/~icwfchan/p4.png The area you have labeled "1" - you need to zoom in closer there, 500mS per division doesn't show much. It seems to be oscillating, but the amplitude is perfectly constant - I bet that is one encoder count. Since you aren't in the USA, I'm assuming your length units are millimeters. In that case, the 500u/div scaling on the pid.0.error trace means 500nm per division (or 0.5 microns per division). That "oscillation" seems to be about 0.8 divisions, or 0.4 microns. 0.4 microns per count would be 2500 counts per millimeter - is that the resolution of your machine? If so, you should probably change the scaling of that scope trace - a scale of 1 or 2 or even 5 microns per division would give you a better view of what is going on. The area you have labeled "2" - that represents the drive and motor lagging behind the position command. Since the vertical scaling is set too high, we can't see how bad the worst-case error is (it is off the top of the screen). The horizontal scaling is also set too slow, so we can't really see the dynamics of the initial acceleration. The sweep rate should be about 10 times faster. The question at the root of problem area "2" is this - is the PID not asking for enough velocity, or is the drive not delivering the velocity that the PID asks for? If the former is true, you probably need to increase P, D, or FF2. If the latter, you need to fix the drive - probably tune the drive velocity loop, with no PID loop in EMC to confuse the issue. Note that you can (and should) use HAL and halscope to do the velocity loop tuning. Run a 0.5 Hz square wave from "siggen" thru a "limit2" block to generate a trapezoidal velocity command, then send that to the DAC and from there to the servo amp. Use a ddt block on the position feedback, or better yet the direct velocity output from the encoder counter, to observe the drive performance. AFTER the servo drive itself is working as well as possible (and you understand its limits, such as accel rate), then you can move on to position control with EMC's position loop. I tend to use a siggen + limit3 block to generate a position command that accelerates, cruises at constant velocity for a while, decelerates to a stop, holds for a while, and then repeats going the other direction. The scope automatically triggers on every repetition, so you can concentrate on changing things with setp and interpreting the results, rather than messing around operating EMC (jogs or whatever). Regards, John Kasunich ------------------------------------------------------------------------------ Check out the new SourceForge.net Marketplace. It is the best place to buy or sell services for just about anything Open Source. http://p.sf.net/sfu/Xq1LFB _______________________________________________ Emc-users mailing list [email protected] https://lists.sourceforge.net/lists/listinfo/emc-users