On Thu, Sep 29, 2011 at 11:59 PM, Martin Patton <[email protected]> wrote:

> >
> > Brian,
> >
> I will do as you suggest and cut a grid.  What did you adjust in the ini
> file?
> Thanks,
> Marty
>


> I cannot recall the exact items to adjust since it was over two years ago
> since I made the correction.  You will most likely not be able to use
> stepconf to make the adjustment.  You will need to hand edit the file (not a
> big deal).  I believe its the scale parameter.  Others will correct me if I
> got this wrong.  The integrator's manual has details on making the accurate
> calculation.
>
> You mentioned that you are using 20tpi rods.  Are these just standard
> threaded rods?  If so, that could be the source of the error.  Getting the
> expected versus actual position and calculating the scale needed.  By doing
> the grid you will find out if the error is in both axes (most likely) or
> not.  By doing a number of points, you will find if the error is linear (tpi
> is slightly off, say 19.95 tpi - likely) or variable (threaded/acme rods are
> not uniform across length - unlikely).
>
> Brian
>
------------------------------------------------------------------------------