On 06.03.2016 09:50, Danny Miller wrote:
> I don't see a reason to view the traffic itself.  I need to go though 
> the manual and read back register values and try writing some regs.  
> It's tedious to do with the panel, and I'd have to unmount the VFD and 
> disable to Modbus to do any panel reads.
> 
> So, reading via modbus would be much more desirable.  Like I need to 
> know what's in the C077 register, and the Intelligent Input Terminal 
> control registers.  And read which IIT reg is activating E12 (which 
> can't be done with modbus disconnected, as it's causing the error somehow).
> 
> Danny
> 
> On 3/6/2016 2:13 AM, Philipp Burch wrote:
>> Hi Danny,
>>
>> I used qModMaster (https://sourceforge.net/projects/qmodmaster/) for
>> low-level Modbus access while I was developing some Modbus hardware.
>> Maybe you can use it to figure out under which circumstances the error
>> occurs.
>> Another option would be to log the traffic (I suppose you are using the
>> serial Modbus connection, not Ethernet) using a Y-cable. You could then
>> compare the commands sent from the Mach3 controller vs. the x200_vfd output.
>>
>> Bye,
>> Philipp
>>
>> On 06.03.2016 09:04, dan...@austin.rr.com wrote:
>>> OK, I think I got it- by just copying x200_vfd from the build dir into 
>>> usr/bin.  I think it was build wrongly the first time I tried that... but 
>>> the code does "go" now.  Which is GREAT!  But it doesn't run the X200.
>>>
>>> Correct me if I'm wrong but it appears that wj200_vfd's modbus bit 
>>> read/writes use addresses offset by -1.  That's the way the code runs and 
>>> it seems to give the correct results in hal monitor.  M3 sets "running" to 
>>> TRUE.  I have all the output bits corrected for the X200- the input bits 
>>> (fwd, reset, trip) are identical in the X200.
>>>
>>> Problem is, as soon as I start, is-alarm bit sets.  The VFD panel says 
>>> "E12", which is "A signal on an intelligent input terminal configured as 
>>> EXT has occurred. The inverter trips and turns OFF the output to the motor"
>>>
>>> I pulled the RJ45 Modbus cable off the VFD and hit Reset, it read 
>>> 0.0="Ready".  Plugged in Rj45 with LinuxCNC running... "E12".
>>>
>>> I can't use the panel to explore the registers.  Once you set the "Modbus 
>>> controls on" DIP switch, the panel input is disabled.
>>>
>>> This is weird.  I was using this VFD under Mach3 and just wrote freq, dir, 
>>> and run.  No "E12" hardware error for that- or with the ModBus unplugged, 
>>> or plugged in but without LinuxCNC running.
>>>
>>> Any ideas?  I'm wondering if I have the Modbus watchdog set (C077) on the 
>>> VFD- I don't think that would cause the Alarm bit to set- that's explicitly 
>>> an EXT error, which should be the physical terminal.  I'd normally say 
>>> "well, then, that error's from the unconnected pin and needs to be 
>>> disabled", but there's no error like that under Mach3.
>>>
>>> Is there a good way to read/write the Modbus coils or regs manually to 
>>> investigate the problem?  Like I say I don't have panel access right now 
>>> because of the physical Modbus switch.
>>>
>>>
>>> Danny

Attachment: signature.asc