Clear counts is not supported for MIB II. You can however clear the RMON
stats counters and RMON history can be helpful if you are wondering about the
rate counters are changing .
Found in the mib defined by RFC 3621
pethPsePortDetectionStatus OBJECT-TYPE
SYNTAX INTEGER {
disabled(1),
searching(2),
deliveringPower(3),
fault(4),
test(5),
otherFault(6)
}
MAX-ACCESS read-only
STATUS current
DESCRIPTION
"Describes the operational status of the port PD detection.
A value of disabled(1)- indicates that the PSE State diagram
is in the state DISABLED.
A value of deliveringPower(3) - indicates that the PSE State
diagram is in the state POWER_ON for a duration greater than
tlim max (see IEEE Std 802.3af Table 33-5 tlim).
A value of fault(4) - indicates that the PSE State diagram is
in the state TEST_ERROR.
A value of test(5) - indicates that the PSE State diagram is
in the state TEST_MODE.
A value of otherFault(6) - indicates that the PSE State
diagram is in the state IDLE due to the variable
error_conditions.
A value of searching(2)- indicates the PSE State diagram is
in a state other than those listed above."
REFERENCE
"IEEE Std 802.3af Section 30.9.1.1.5
aPSEPowerDetectionStatus"
::= { pethPsePortEntry 6 }
pethPsePortPowerClassifications OBJECT-TYPE
SYNTAX INTEGER {
class0(1),
class1(2),
class2(3),
class3(4),
class4(5)
}
MAX-ACCESS read-only
STATUS current
DESCRIPTION
"Classification is a way to tag different terminals on the
Power over LAN network according to their power consumption.
Devices such as IP telephones, WLAN access points and others,
will be classified according to their power requirements.
The meaning of the classification labels is defined in the
IEEE specification.
This variable is valid only while a PD is being powered,
that is, while the attribute pethPsePortDetectionStatus
is reporting the enumeration deliveringPower."
REFERENCE
"IEEE Std 802.3af Section 30.9.1.1.6
aPSEPowerClassification"
::= { pethPsePortEntry 10 }
And this found in ENTERASYS-POWER-ETHERNET-EXT-MIB
etsysPsePortPowerUsage OBJECT-TYPE
SYNTAX Gauge32
UNITS "milliwatts"
MAX-ACCESS read-only
STATUS current
DESCRIPTION
"Actual power consumption measured in real-time."
::= { etsysPsePortPowerManagementEntry 2 }
Hope this helps,
Ernie Eaton
From: Mark Lamond [mailto:[email protected]]
Sent: Tuesday, February 23, 2010 4:35 PM
To: Enterasys Customer Mailing List
Subject: [enterasys] DFE Platinum - Clear Counters & Interface POE status OID
Hi everyone,
On the DFE Platinum v6.11.01 does anyone know of a way to zero the MIB2
interface counters as displayed by the "show port counters" command?
Also, I'm building a few Flexviews in Netsight v3.1.3.37 and looking for the
OID that will show me if an interface is delivering POE or not? You can obtain
this information on the command line with the "show port inlinepower" command.
Many thanks,
Mark Lamond
* --To unsubscribe from enterasys, send email to
[email protected]<mailto:[email protected]> with the body: unsubscribe enterasys
[email protected]
---
To unsubscribe from enterasys, send email to [email protected] with the body: