Hi Vincent,

1) I think 4339:05 relates to CoE object 0x10F3:05.  Set the value to 0.

Try setting it manually via the ethercat command line before starting your app 
to start with.  If that helps, set it via your app before going active.


2) Some slave modules support diagnostic messages.  These are on the slave 
itself, under the 0x10F3 CoE index.  The EtherLab master doesn't have a 
framework to automatically read them and It's a reasonably big topic to get 
your head around.  Here's a starting point:
https://infosys.beckhoff.com/english.php?content=../content/1033/el34x3/1859331211.html&id=210180382886825810

Note: a lot of diagnostic ID's are module specific.  They can be found in the 
modules esi file (Beckhoff EL5xxx.xml) under the <DiagMessages> node.  There's 
only around 11 for this module, but the page above lists common diag messages.


3) I have found that for Beckhoff modules that only support fixed PDO entries, 
if you get the PDO configuration wrong (e.g. your cstruct was generated for an 
older revision of the module) you will get errors the first time you apply the 
config (listed in dmesg).  The modules PDO settings are however updated with 
the new, but incorrect information.  Internally the module will ignore these 
mistakes and use its fixed PDO config.  Note: this is why you should only use 
the cstruct command after a clean boot of a slave.

If you restart your app, without repowering the slave, then no errors will be 
reported this second time because the PDO configuration you are applying now 
matches what the slave is reporting, even though it's wrong.

I have found some modules do not get to OP when they have these PDO config 
errors, though usually I find they get to SAFEOP + Error.

I'm just speculating that this particular module may have an issue with 
applying an incorrect PDO configuration in combination with applying SDO 
configuration.


4) As a new thought, what SDO configuration calls are you making?  This module 
supports CoE complete access.  If you are setting multiple subindex entries 
under one index, try setting it as a complete access call instead.


Note: we also use the EL5101.  For this and most other modules we also call the 
reset command as our first SDO config item to ensure there are no unexpected 
configuration options set, e.g.:
ecrt_slave_config_sdo32(dev->slaveConfig, 0x1011, 0x01, 0x64616F6C);

Graeme.


From: BUSSIERES Vincent <vincent.bussie...@hemeria-group.com>
Sent: Friday, 15 October 2021 12:00
To: Graeme Foot <graeme.f...@touchcut.com>; etherlab-users@etherlab.org
Subject: RE: strange behaviour with sdo configuration


Thank you Graeme for these thoughts.

I used a similar module (EL5101), I hadn't this problem but pdo assignment was 
different. I used cstruct command to get pdo informations.



1) With which value should I set the value in index 4339:5 ?



2) How can I see diagnostic messages ? with dmesg?



3) Is it possible to encounter PDO error only during sdo configuration? I don't 
understand why at the second start there is no PDO error ?



Regards

________________________________
De : Graeme Foot <graeme.f...@touchcut.com<mailto:graeme.f...@touchcut.com>>
Envoyé : jeudi 14 octobre 2021 23:36
À : BUSSIERES Vincent; 
etherlab-users@etherlab.org<mailto:etherlab-users@etherlab.org>
Objet : RE: strange behaviour with sdo configuration


Hi Vincent,



I don't have a module to play with so no real idea.  But here's some thoughts:



1) The Beckhoff esi file "Beckhoff EL5xxx.xml" file shows setting the value in 
index 4339:5 to 0000 on transition from Init to PreOp:

            <InitCmd>

              <Transition>IP</Transition>

              <Index>4339</Index>

              <SubIndex>5</SubIndex>

              <Data AdaptAutomatically="1">0000</Data>

            </InitCmd>



You could try setting this value before activating your master.  I think 4339 
is decimal so relates to 0x10F3:05.



0x10F3:05 is the Diagnostics Flags value.  This is 0x0001 by default which 
reports the presence of a DiagMessage as an emergency.





2) The module supports diagnostics.  Check the Diagnostic messages for issues 
during the startup with and without the SDO configs.





3) On first application start from a cold boot, without any of the SDO config 
calls, check the dmesg log for any errors with assigning the PDO's for the 
module.  It may be that if PDO errors are encountered along with the SDO config 
calls the module stays in PREOP + Error.  But without the SDO config calls it 
may get to OP OK.



On the second start the PDO's will already have been changed so the master / 
slave won't report any errors (even though the module will ignore the changes 
internally as they are fixed PDO's).  Due to no PDO errors being reported the 
second time it may be why the SDO config calls succeed.





Regards,

Graeme.





From: Etherlab-users 
<etherlab-users-boun...@etherlab.org<mailto:etherlab-users-boun...@etherlab.org>>
 On Behalf Of BUSSIERES Vincent
Sent: Friday, 15 October 2021 09:11
To: etherlab-users@etherlab.org<mailto:etherlab-users@etherlab.org>
Subject: [Etherlab-users] strange behaviour with sdo configuration



Dear Etherlab users,



I bought a Beckhoff EtherCAT Terminal, 2-channel encoder interface EL5102. This 
product has just been released.

I encounter problems when I configure sdos with « ecrt_slave_config_sdo8 » or « 
ecrt_slave_config_create_sdo_request » functions called before « 
ecrt_master_activate » as for my other slaves.

This slave doesn't switch at the OP State and stay in PRE-OP State with error « 
E » :



"1 0:1 PREOP E EK5102 2K. Inc. Encoder 5V (RS422, TTL)"



I noticed that when I comment sdo configuration methods and run my application, 
slave switches to OP State.

After being switched one time to OP, if I uncomment configuration methods and 
run once again my application, slave behaviour seems to be OK, slave switches 
to OP State.



I don't understand why after the fisrt boot, there is such a problem ?