Would it be possible to loop the 4-20 ma output through a 4-20 ma input and
alarm it in the ain block? Another way might be to add a low value resistor
in the loop and monitor a voltage drop across it with an FBM 02.This would
take an extra input for each loop. I do not know what type of isolation
problem, if any, you might run into. I would wire it to a different FBM. If
this would work it would save you from
having to install a position transmitter on the valve.
Loyd Greer
---- Original Message -----
From: Rick Rys <[EMAIL PROTECTED]>
To: Foxboro DCS Mail List <[EMAIL PROTECTED]>
Sent: Thursday, May 10, 2001 6:52 PM
Subject: RE: Open-loop detection on analog output cards
> Let's assume you have an FBM 04 with ECB type 2, and a simple AIN, PID(A),
> AOUT analog control loop. Next you remove the wiring at the FBM terminal
> for the 4-20ma output for this channel.
>
> The CP is good, the fieldbus is good, and the FBM is good. ECB Failsafe is
> not enabled. The field wiring is bad (open), however, and the valve is
> getting 0ma and thus going to it's failure state. You will likely be
> getting some alarms soon enough, but I understand why you might want to
get
> an alarm immediately. This might be possible with intelligent
transmitters,
> but it is my understanding that the FBM04 is not smart enough to identify
a
> single open loop output. Inputs would be caught by out of range, but I
> don't think there is any way to detect a bad output short of a valve
> position transmitter with some type of deviation alarming scheme. In the
> AOUT block the BAO when set to 1 has alarming looking at BAD (BO193AX
Block
> Book). BAD is set from the OPSTAT of the ECB block (with some logic I
could
> not find), but the ECB is only setting the BAD based on communication
> related errors (see ECB Block description) and not disconnected output
> wires. You can look at BAD, OPSTAT, or ECBSTA to verify that nothing is
> showing as bad. Maybe someone else could verify this behavior as I didn't
> check it on real hardware.
>
> Rick Rys
> R2 Controls
>
>
>
> -----------------------------------------------------------------------
> This list is neither sponsored nor endorsed by the Foxboro Company. All
> postings from this list are the work of list subscribers and no warranty
> is made or implied as to the accuracy of any information disseminated
> through this medium. By subscribing to this list you agree to hold the
> list sponsor(s) blameless for any and all mishaps which might occur due to
> your application of information received from this mailing list.
>
> To be removed from this list, send mail to
> [EMAIL PROTECTED]
> with "unsubscribe foxboro" in the Subject. Or, send any mail to
> [EMAIL PROTECTED]
>
-----------------------------------------------------------------------
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur due to
your application of information received from this mailing list.
To be removed from this list, send mail to
[EMAIL PROTECTED]
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]