You could buy our Event Driven Scripts product. This product receives I/A
Series Alarm Messages and applies a filter to the message. If the message
passes the filter, a user specified script is run.
Thus, you could have a filter line for each alarm or alarm group (the
filtering is pretty sophisticated) and run a particular script for each.
This script could set the digital output that you request.
This software is the core of FoxPage and it can be used to trigger any
number of interesting things based on an I/A Series message. The message
types supported are Process Alarms, SOE messages, Sequence Block messages,
System Monitor messages, and Operator Action Journal messages.
The way we invoke your script is that we create a script that contains a
number of environment variables. These environment variables contain one
field from the message each. Thus, your script can be passed pieces of the
message for process, i.e., we parse the message for you.
Since I can't send attachments to the list (and don't want to be banned for
"selling"), I'll send you some info separately.
BTW: The PSS is complete, but not yet on the web site. The part numbers are
in the IQS catalog. I've put part of the PSS below.
PART NUMBERS
The following table identifies the various FoxPage Part Numbers.
Q0301JE - FoxPage for SUN Solaris (US Only)
* FoxPage manual and installation diskette
* Electronic messaging manual, license, installation CD-ROM and annual
maintenance agreement (It is up to the customer to renew this agreement with
the software manufacturer or Foxboro through a maintenance agreement.)
* MultiTech modem
* Modem (25 male - 25 male) cable
Q0301JF - FoxPage for Windows NT (US Only)
* FoxPage manual and installation diskette
* Electronic messaging manual, license, installation CD-ROM and annual
maintenance agreement (It is up to the customer to renew this agreement with
the software manufacturer or Foxboro through a maintenance agreement.)
* MultiTech modem
* Modem (9 female - 25 male) cable
Q0301JG - FoxPage for SUN Solaris (International)
* FoxPage manual and installation diskette
* Electronic messaging manual, license, installation CD-ROM and annual
maintenance agreement (It is up to the customer to renew this agreement with
the software manufacturer or Foxboro through a maintenance agreement.)
Q0301JH - FoxPage for Windows NT (International)
* FoxPage manual and installation diskette
* Electronic messaging software manual, license, installation CD-ROM
and annual maintenance agreement (It is up to the customer to renew this
agreement with the software manufacturer or Foxboro through a maintenance
agreement.)
Q0301JJ - Event Driven Scripts for SUN Solaris
Event Driven Scripts manual and installation diskette
Q0301JK - Event Driven Scripts for Windows NT
Event Driven Scripts manual and installation diskette
REQUIREMENTS
Hardware
* I/A Series AP/AW/WP51 A/B/C/D/E (Version 4.3/6.1 and later)
* I/A Series AW70 (Version 6.2 and later)
* Appropriate Serial Expansion Card
* 50 Series disk space requirements - 4MB free in the /usr and 3MB
free in the /opt partitions.
* 70 Series disk space requirement - 7MB free on the hard drive.
Services
* Installation is not included. Local area paging systems require
application engineering or field service support, which must be quoted
separately.
Paging System Requirements
* Numeric Pagers - Numeric paging systems must use Dual Tone Multi
Frequency (DTMF).
* Alphanumeric Pagers - Alphanumeric paging systems must use Telocator
Alphanumeric Protocol (TAP) or Page Entry Terminal Protocol (PET).
Regards,
Alex Johnson
The Foxboro Company
10707 Haddington
Houston, TX 77043
713.722.2859 (v)
713.722.2700 (sb)
713.932.0222 (f)
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>
-----Original Message-----
From: [EMAIL PROTECTED]
[SMTP:[EMAIL PROTECTED]]
Sent: Wednesday, May 03, 2000 6:27 AM
To: [EMAIL PROTECTED]
Subject: RE: External Horn For Process Alarms
Alex-
Thanks for the info on the CAG - I definitely misunderstood its use.
Manufacturing installed a system that can broadcast voice messages
through
the building and they want to use it to tell the operators exactly
what is
in alarm. The system can take a large number of digital inputs (a
DO from
the Foxboro) and it triggers a preset voice message. Currently all
of our
emergency shutdown alarms are priority 1 which trips one horn tone.
Since
they have no idea which process is in alarm, they want to separate
this out,
so when process 1 has an emergency sd alarm one DO is tripped, and
when
process 2 has an emergency sd a different DO is tripped, same goes
for all
other types of alarms. I wasn't aware of what they were trying to
do until
after they purchased the system so now I am trying to come up with a
scheme
that will work. Currently the system is designed for 32 separate
alarm
messages, but they are talking of increasing it. I was hoping that I
could
do this by using the horn.cfg file since that is the standard way we
handle
external horns but it sounds like it will not work this way. Any
ideas?
Thanks-
Marci Sewell
Process Automation and Control
115 Bldg, Mail 032
ph: (517)496-5071 page: (517)926-1487
email: [EMAIL PROTECTED]
-----Original Message-----
From: Johnson,Alex [mailto:[EMAIL PROTECTED]]
Sent: Tuesday, May 02, 2000 4:30 PM
To: Foxboro DCS Mail List
Subject: RE: External Horn For Process Alarms
The CAG is good for two things:
1) Silencing all horns on the WPs in the CAG when the horn is
silenced
on any WP in the group.
2) Clearing an alarm from all WPs in the CAG when the alarm is
cleared
from any other WP in the group.
When the horn silence button is pressed on an annunciator keyboard
(it's
sometimes (mis)labeled ACK), all horns on that WP (internal and
external)
are silenced regardless of priority.
So, to get to your questions:
1) what happens [to the horns -ed] when one of the WP's [in the
CAG
-ed] is turned off?
Basically, the answer is nothing special. Internal horns are
silenced because they are now off too. External horns shared with
another WP
continue to be driven by that WP. External horns driven uniquely by
the WP
that is now off, remain in their last state - blaring away perhaps.
2) If they are all members of the same Common alarm group, will
the
backup WP take over for the downed WP and sound its alarms for it?
The surviving WP will sound the horns that it is configured
for when
it receives an alarm. If the WPs share external horns, the surviving
WP will
of course drive them. If the WPs have a disjoint set of horns, the
"dead"
WPs horns just hang there.
3) Or do I lose 5 of my alarm horns?
Well, not literally, but they will no longer be driven
assuming that
on the "dead" WP works with them.
3) [I -ed] want to have 64 different external horns, is it
possible to
do this through the horn.cfg file [? -ed]
No, the system supports only six external horns (5 for
process
alarms and 1 for system alarms).
4) or do I have to come up with something else?
You need something else.
Can you explain what you want to accomplish? Maybe there is another
route.
Regards,
Alex Johnson
The Foxboro Company
10707 Haddington
Houston, TX 77043
713.722.2859 (v)
713.722.2700 (sb)
713.932.0222 (f)
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>
-----Original Message-----
From: [EMAIL PROTECTED]
[SMTP:[EMAIL PROTECTED]]
Sent: Tuesday, May 02, 2000 2:55 PM
To: [EMAIL PROTECTED]
Subject: RE: External Horn For Process Alarms
I have a question about the horn.cfg file when used to sound
an
external
horn. I am going to use an example to pose my question.
If I have 3 WPs, each specifying different external horns to
sound
on
Priority 1 -5 alarms (so I have a total of 15 digital
outputs), what
happens
when one of the WP's is turned off? If they are all members
of the
same
Common alarm group, will the backup WP take over for the
downed WP
and sound
its alarms for it? Or do I lose 5 of my alarm horns?
Another related question:
If I have 3 WPs, but want to have 64 different external
horns, is it
possible to do this through the horn.cfg file or do I have
to come
up with
something else?
BTW, I am not the nutjob who thinks having 60 different
external
horns in
one building is a good idea. I unfortunately, was asked to
try to
implement
it.
Thanks-
Marci Sewell
Process Automation and Control
115 Bldg, Mail 032
ph: (517)496-5071 page: (517)926-1487
email: [EMAIL PROTECTED]
-----Original Message-----
From: Duc M Do [mailto:[EMAIL PROTECTED]]
Sent: Tuesday, May 02, 2000 3:06 PM
To: Foxboro DCS Mail List; Foxboro DCS Mail List
Subject: RE: Process Alarms
At 02:48 PM 5/2/00 -0400, Johnson,Alex wrote:
>2) Use a PC as your "alarm printer" and one of several
3rd
party
>packages to capture the alarms.
We do something similar. We feed all the process alarms (and
system
alarms, too, for that matter) to a VAX. Our friendly VAX
guru sets
up
automatic capturing and parsing of the alarms into process
area
specific files (text files, one file per day) and put them
on a web
server. The process people can grab them at their leisure
and do
whatever with them. These files are kept on the web server
for 3
months
and then archived to CD-ROM for who knows how long.
Duc M. Do
Dow Corning Corp.
Carrollton Plant
Carrollton, KY, US
-----------------------------------------------------------------------
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur due to
your application of information received from this mailing list.
To be removed from this list, send mail to
[EMAIL PROTECTED]
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]