Rory,

Did you get your loop fixed?

Regards,

Alex Johnson
The Foxboro Company
10707 Haddington
Houston, TX 77043
713.722.2859 (v)
713.722.2700 (sb)
713.932.0222 (f)
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> 


        -----Original Message-----
        From:   Johnson,Alex [SMTP:[EMAIL PROTECTED]]
        Sent:   Sunday, June 04, 2000 2:42 PM
        To:     Foxboro DCS Mail List
        Subject:        RE: Foxboro single loop controller to I/A

        Rory,

        Sounds like your loop needs tuning to me. Steve Elwart brought the
following
        excerpt from Control Engineering to my attention. Perhaps, these
values will
        put you in the right ball park.

        I am by no means a tuning expert, but these should get you in the
ball park.


        Send any thanks to Steve and Control Engineering.


        Regards,

        Alex Johnson
        The Foxboro Company
        10707 Haddington
        Houston, TX 77043
        713.722.2859 (v)
        713.722.2700 (sb)
        713.932.0222 (f)
        [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> 


        Control Engineering readers consistently indicate loop analysis and
PID 
        tuning articles are among the most useful articles we provide. But 
        establishing valid PID tuning parameters requires determining
process 
        dynamics, and that's seldom possible until the process is up and
        operating. 

        However, that doesn't mean loops must remain in manual until process

        dynamic testing is completed. Here's a set of very conservative PID 
        settings that can be initially used, but will normally result in
sluggish 
        response...but they come with no guarantees.

        Gain is in proportional gain (Delta percent output / Delta percent
input)
        Integral is in repeats per minute
        Derivative is in minutes

        Loop Type: 
        Flow         Gain =  3    Integral = 30      Derivative = 0
        Temperature  Gain =  1.25 Integral = 0.2     Derivative = 0.05
        Level        Gain =  2    Integral = min.    Derivative = 0
        Gas pressure Gain = 10    Integral = min.    Derivative = 0

        Note: In "Foxboro-ese", 

           Proportional Band is 1/Gain * 100 and 
           Integral is in minutes per repeat (not repeats per minute).  

           Therefore a gain of 3 is equal to a PBand of 33.




                -----Original Message-----
                From:   Loupe, Rory [SMTP:[EMAIL PROTECTED]]
                Sent:   Tuesday, May 30, 2000 4:36 PM
                To:     FOXBORO List (E-mail)
                Subject:        Foxboro single loop controller to I/A

                We recently moved control of a boiler from a Foxboro single
loop
        controller
                to the I/A DCS.  The field instrumentation (steam flow
transmitter,
        water
                flow transmitter, level transmitter and water flow control
valve)
        and piping
                remained the same.  We tried setting up the DCS control
scheme the
        same as
                the single loop controls with little success.


                The control scheme is as follows:
                We have a standard PID (setup as a PI controller) level
controller
        with the
                output of the controller scaled the same as the flow
transmitter.
        The level
                tranmitter is setup for 0 to 100 percent.  The setpoint of
the level
                controller is local and set at 50 percent.

                The output of the level controller is added to K times the
steam
        flow out of
                the boiler.  The K factor is 0 to 1.5.  The old single loop
        controller had a
                K factor of 1 which basically added the output of the level
        controller to
                the steam flow out of the boiler.  This calculated value is
the
        setpoint of
                the flow controller.

                We have a standard PID (setup as a PI controller) flow
controller
        which
                controlls the water flow valve.  This vavle regulate the
amout of
        water into
                the boiler.  The setpoint of the control is equal to the
calculated
        value
                Level_Controller.OUT + (K * Steam_Flow.PNT).

                The steam flow stays relatively constant.  It's the
calculated
        setpoint
                (using the level controller outpur and steam flow) that
seems to be
                swinging.  I believe this is swinging because the level
controller's
        output
                is swinging.

                Has anyone move control of a boiler from a Foxboro single
loop
        controller to
                the Foxboro I/A DCS?  Any help or incite would be much
appreciated.

                Thanks,
                Rory Loupe
                Process Control Engineer
                Rhodia, Inc.
                Baton Rouge, LA




-----------------------------------------------------------------------
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]

Reply via email to