Jack,
In a similar vein, if you have alarms that are less important when the 
pump (or other piece of key equipment) is down you can connect the 
alarm priority -- ie. gland seal is a priority 1 alarm when the pump is 
running, but a priority 5 alarm when the pump is off.  You can also use 
the alarm inhibit mask to selectively inhibit alarms -- ie. pump box 
level hi-hi is never inhibited, but hi, lo, and lo-lo are inhibited 
when pump is not running.
Regards,
Kevin FitzGerrell
Systems Engineer

----- Original Message -----
From: "Schouten, Frits JF" <[EMAIL PROTECTED]>
Date: Monday, September 25, 2000 8:40 am
Subject: RE: Can alarms be grouped to give a single alarm?

> Hi Jack,
> 
> what about inhibiting the flowon alarms?
> Like when the pump stops you inhibit the low flow etc with the 
> pump status bit or so.
> We here at NZSteel are implementing, where ever we can, an alarm 
> inhibit scheme to the extent that halve a plant could be inhibited 
> when appropriate. You have to think of a smart scheme of lifting 
> the inhibit without regenerating nuisance alarms.
> There is nothing worse than nuisance alarms from equipment that is 
> turned off or being started.
> I've found that, with a lot of input from operators, you can set 
> up a really good working alarm inhibit scheme.
> 
> Cheers,
> Frits Schouten.
> BHP-NZSteel.
> 
> 
> > -----Original Message-----
> > From:       [EMAIL PROTECTED] 
[SMTP:[EMAIL PROTECTED]]
> > Sent:       Saturday, September 23, 2000 6:25 AM
> > To: [EMAIL PROTECTED]
> > Subject:    Can alarms be grouped to give a single alarm?
> > 
> >      I would like to know if alarms from different blocks can be 
> grouped to 
> >      give a single alarm.
> >      
> >      For example, a pump stops working.  I could get a pump 
> status alarm, a 
> >      lo flow alarm, a hi output alarm, and a hi level alarm.  
> All of these 
> >      alarms represent one condition.  Is there anyway to make 
> these give 
> >      just one alarm without using logic blocks all over the place?
> >      
> >      Or, if logic blocks are the only way, what is the most 
> efficient way 
> >      to accomplish it?
> >      
> >      Or, should I just consider getting rid of some of those alarms?
> >      
> >      I looked in B0193RV - Workstation Alarm Management, but 
> didn't see 
> >      anything obvious.
> >      
> >      Thanks for the help.
> >      
> >      Jack Ziegler
> >      Sunoco Chemicals
> >      Frankford Phenol Plant
> >      215-537-2422
> > 
> > 
> > 
> 


-----------------------------------------------------------------------
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]

Reply via email to