Thanks Yuri. As you can see I was already bumping the Min so I  was effectively 
increasing the threads per disk as you suggest. I don't see nsdThreadsPerDisk 
in the config output, nor is it documented. I know it was before.

Interestingly, increasing the threads didn't really help, and in some cases 
made things worse. I settled on 256 threads and 32 threads per queue, with a 
ratio of 1. This gives me 4 large and 4 shall queues.

Regardless of the number of queues and threads I toss at it, I still see a 
number of queues with pending request in the 100's.

Waiters shows I/O waiters in the 200-300ms range, but the flash system (not IBM 
btw) still reports latency below 1ms.

Not sure where the bottleneck is. Perhaps it's the disk subsystem in Linux. Not 
sure how much can tell.

Back to playing whack-a-mole.

Bob Oesterlin
Sr Storage Engineer, Nuance HPC Grid

_____________________________
From: Yuri L Volobuev <[email protected]<mailto:[email protected]>>
Sent: Tuesday, January 12, 2016 3:58 PM
Subject: Re: [gpfsug-discuss] Advice on NSD Thread tuning, moving from Disk to 
Flash
To: gpfsug main discussion list 
<[email protected]<mailto:[email protected]>>



If you want to have more NSD worker threads running, the recommended way to do 
this is increase nsdThreadsPerDisk, and also increase nsdMaxWorkerThreads. Make 
sure you have enough pagepool for all of the new threads though. You can also 
achieve a similar result by increasing nsdMinWorkerThreads, which would render 
threads-per-disk logic irrelevant, although that's not how this parameter is 
normally used.