The hospital I used to work for had Halon all through their data center, and 
one day back in the mid 90's they had an accidental dump.  (The cause was never 
determined.)

I was told that the cost to recharge the system was $50,000, and that it would 
be the last time they would be able to get halon.  It also took a week or so to 
schedule the work, so they were without fire protection for that period.  Their 
solution was to add a second halon canister to each zone, with a transfer 
switch.  That way, they could be protected in case they had another dump, and 
recharge was unavailable for a protracted period.

Hopefully they've found a better solution by now.

> -----Original Message-----
> From: IBM Mainframe Discussion List [mailto:[EMAIL PROTECTED]
> Behalf Of Ed Finnell
> Sent: Wednesday, June 22, 2005 12:31 PM
> To: [email protected]
> Subject: Re: [IBM-MAIN] HALON et al
> 
> 
>  
> In a message dated 6/22/2005 10:56:15 A.M. Central Standard Time,  
> [EMAIL PROTECTED] writes:
> 
> Both  Halon (which was bad for the Ozone layer) and a more 
> environmentally  friendly replacement 
> 1,1,1,2,3,3,3-heptafluoro-propane 
> (manufactured under  names such as HFC-227ea, FM-200, FE-227) have a 
> minimum concentration at  which they will suppress fires, and 
> a higher 
> concentration at which they  become toxic.  If I remember 
> correctly, the 
> size of the effective,  nontoxic range is not that large, and 
> smaller for 
> Halon than  HFC-227ea.  IF the fire suppression system is properly  
> 
> 
> 
> >>
> There's a Federal tax of $45/lb on Halon in the US. This is
> to encourage alternatives. Before we could get changed out
> our Halon provider hit the discharge button instead of the test
> button and blew out the ceiling tiles in the print shop. Just
> got it cleaned up good and recertified and danged if the welders
> down the hall let it all cut loose and the the ventilation system
> sucked it in threw an open window(for special forms don't ya know)
> and blew it out again.
>  
> The low bid on a replacement was a water mist system and just
> couln't get past the water and elctricity don't mix. Still Halon,
> although with recycled mix it's down to about $42/lb no tax.
>  
> There was a field replacement of blue for brown(tan really) 
> bus and tags  
> that IBM did for upgrades and replacements. The blue 
> evidently react with Halon  
> to produce a carcinogen in a real fire.
>  
> Everything went to brown except a couple of 3088s and they 
> couldn't find  any 
> short browns anywhere....  
> 
> ----------------------------------------------------------------------
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to [EMAIL PROTECTED] with the message: GET IBM-MAIN INFO
> Search the archives at http://bama.ua.edu/archives/ibm-main.html
>
--------------------------------------------------------

If you are not an intended recipient of this e-mail, please notify the sender, 
delete it and do not read, act upon, print, disclose, copy, retain or 
redistribute it. Click here for important additional terms relating to this 
e-mail.     http://www.ml.com/email_terms/
--------------------------------------------------------

----------------------------------------------------------------------
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to [EMAIL PROTECTED] with the message: GET IBM-MAIN INFO
Search the archives at http://bama.ua.edu/archives/ibm-main.html

Reply via email to