On 08/18/2014 08:04 AM, Nims,Alva John (Al) wrote:
> Oh, you reminded me of the "Big Red Button" or "Big Red Pull" which was NOT a 
> POR, it was for a few systems a Power Off with NO chance of a Power On 
> anytime soon, because a CE would have to come in and replace the circuit that 
> a knife just sliced through to do the Emergency Power Off that the "Big Red 
> Button" just forced through.
>
> Al Nims
> Systems Admin/Programmer 3
> Information Technology
> University of Florida
> (352) 273-1298
>
> -----Original Message-----
> From: IBM Mainframe Discussion List [mailto:[email protected]] On 
> Behalf Of Phil Smith
> Sent: Friday, August 15, 2014 6:05 PM
> To: [email protected]
> Subject: Re: Mainframe jargon and acronyms wasRe: AMBLIST, AMASPZAP, and UNIX 
> Program Objects
>
> Let's not forget "Poughkeepsie reset" and "BRS" (Big Red Switch), both 
> meaning a POR!
>
>
>
>

The Emergency Power Off switch interlock on all IBM processor models
that we had over a period of several decades was only a mechanical
interlock on the EPO switch itself -- at least so on all our processors
where it was accidentally or out of ignorance used (it was never
deliberately used).  Although it cuts all processor power immediately
and does not allow for normal power-down sequencing or delayed shutdown
of processor cooling, I can't recall a case where damage was done by use
of the processor EPO, although the IBM CE was always called in to check
out the system afterwards.  At least on some processor model (360/65?) ,
the beginning of the diagnostic procedure was to just reset the
mechanical trip in the switch to reset the EPO switch, do a power-up and
see if everything worked.  My recollection is that after one EPO
incident our in-house IBM CE did something  to disable the EPO
mechanical lockout on the processor EPO switch, so if the EPO were
tripped when the CE was off-site and SysProgs got in before the CE he
could advise them to reset it and try to power-up while he was in route. 

Somewhere along the line people seemed to realize that use of the
processor EPO was actually a cleaner way to shut down the system than a
power failure (utility power failure without a UPS or a UPS failure), as
power failures can involve spikes and other abnormal voltages on one or
more power phases as the failure is occurring.  Our normal recovery
procedure from a power failure at least from the 1980's on was to call
in System Support staff and the IBM CE (in case he was needed), wait for
stable power to be restored, then start power-up of all devices and see
if anything failed to come back up, then advise the CE what units had
failures.  We occasionally had some devices that wouldn't power up, but
it was usually DASD or some other I/O equipment and not the processor
itself.  It never made sense to treat use of the processor EPO as a more
serious event than a power failure and force a CE to be on-site to start
recovery from the EPO when that was not the case for a power failure.

-- 
Joel C. Ewing,    Bentonville, AR       [email protected] 

----------------------------------------------------------------------