Jake,
If you don't have access to IBM TechDocs, I can send the PDF version to you 
direct. There are some important considerations if you are using the z14 ZR1 as 
a coupling facility. This is covered in detail in the Tech Doc.


Short answer. customer supplied UPS. 

Here is some text I have cut from the TechDoc I referenced:

The Internal Battery Feature (IBF) is an optional feature on many of the IBM Z 
family processors. The IBF provides a local uninterrupted power source
and further enhances the robustness of the power design present in the 
mainframe and increases a mainframe’s immunity to power line disturbance
. It provides battery backup power to preserve processor data during a loss of 
power on all power feeds from the computer room. The IBF can hold 
power briefly during a brownout, or for orderly shutdown if there is a longer 
outage. IBM announced the IBM z14 ZR1 in April 2018. The announcement included 
information about the single 19” frame that houses the ZR1hardware components 
as well as a new Feature Code (FC), FC 0617 – 16U Reserved, which allows 
customers to install components other than ZR1 hardware inside of the 19” rack 
given that it meets a set of criteria for the space. 
The ZR1 will not be available with an IBF; clients requiring a battery backup 
solution must consider an alternative battery backup solution when planning for 
the ZR1
. 
Although the IBF is offered on the dual frame z14, it will not be offered as a 
feature option for the IBM z14 Model ZR1 processor. Clients with sensitive data 
on a ZR1 will need to explore an external industry - standard solution such as 
an Uninterrupted Power Supply (UPS) to address concerns regarding back -
up generator lag - time.

IBM ZR1 Considerations. There is no IBF feature for any z14 Model ZR1 . Battery 
backup, such as an external UPS solution or floor wide UPS solution, can be 
used to provide power resiliency to the ZR1. A UPS installed into the 16U 
Reserved Area will only be able to provide battery backup to other 
hardware installed in this area; ZR1 hardware, outside of the 16U Reserved 
area, cannot be powered from a UPS installed in the 19” rack.

Battery backup power from an external UPS solution or floor wide UPS solution 
can provide the ZR1 power in case of a brownout, or in the case of a longer 
power outage, it will provide time to properly bring down components running in 
the ZR1. This can become particularly important when Coupling Facilities (CF) 
are housed inside of the CPC.

----------------------------------------------------------------------