https://issues.apache.org/jira/browse/PLC4X-156?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=16988980#comment-16988980
 ] 

Alvaro del Castillo commented on PLC4X-156:
-------------------------------------------

Cool, than you very much guy. I have read it and it looks good. Are you doing 
code review in the project? Give me 2 days to test it and return real feedback.

> The unitId (device id/slave id) is hardcoded to 0 which is the broadcast id 
> in modbus
> -------------------------------------------------------------------------------------
>
>                 Key: PLC4X-156
>                 URL: https://issues.apache.org/jira/browse/PLC4X-156
>             Project: Apache PLC4X
>          Issue Type: Bug
>          Components: Driver-Modbus
>            Reporter: Alvaro del Castillo
>            Assignee: Christofer Dutz
>            Priority: Critical
>              Labels: config
>             Fix For: 0.6.0
>
>         Attachments: Plc4XModbusProtocol.java
>
>
> Trying to use the modbus driver, it is always trying to read and write from 
> the slave 0 in the modbus slave/server. This identifier is the one used for 
> broadcasting reads and writes to all the slaves in the modbus network. In 
> modbus TCP this identifier is not needed, but it is needed to support legacy 
> devices.
> And testing with with some modbus serves like:
> [https://pypi.org/project/pyModSlave|https://pypi.org/project/pyModSlave/]
> and in the second case, if you try to read a register:
> {noformat}
> 2019-11-27 08:29:29,837 ERROR modbus.handle_request Thread-1 invalid request: 
> Function 3 can not be broadcasted{noformat}
> This unitId should be a param but if it must be hardcoded, changing it to *1* 
> is a fix. But in some cases, you could need a 
> specific id to connect to a device. For example, for the XY-MD02 sensor 
> connected via serial to a Modbus TCP client, in order to read the values from 
> the sensor you need to provide the right device id (in this case is also 1, 
> but it could change).
> The unitId is defined in:
> [https://github.com/apache/plc4x/blob/develop/plc4j/protocols/modbus/src/main/java/org/apache/plc4x/java/modbus/netty/Plc4XModbusProtocol.java#L92]
> I have tested in 0.4.0 release that changing the unitId to *1* fixes the 
> problem with modbus servers. I have attached the file with this minor 
> modification.
> I can send a PR if you find the fix useful.
> Thanks!
>  
>  



--