Sebastian Wiendl created PLC4X-163:
--------------------------------------

             Summary: Netty OutOfDirectMemoryError
                 Key: PLC4X-163
                 URL: https://issues.apache.org/jira/browse/PLC4X-163
             Project: Apache PLC4X
          Issue Type: Bug
          Components: Util-Scraper
    Affects Versions: 0.5.0
         Environment: Ubuntu 16.04 LTS
Java 1.8.0_201
{code}$ java -XX:+PrintFlagsFinal -version | grep -iE 
'HeapSize|PermSize|ThreadStackSize'
     intx CompilerThreadStackSize                   = 0                         
          {pd product}
    uintx ErgoHeapSizeLimit                         = 0                         
          {product}
    uintx HeapSizePerGCThread                       = 87241520                  
          {product}
    uintx InitialHeapSize                          := 132120576                 
          {product}
    uintx LargePageHeapSizeThreshold                = 134217728                 
          {product}
    uintx MaxHeapSize                              := 2092957696                
          {product}
     intx ThreadStackSize                           = 1024                      
          {pd product}
     intx VMThreadStackSize                         = 1024                      
          {pd product}
java version "1.8.0_201"
Java(TM) SE Runtime Environment (build 1.8.0_201-b09)
Java HotSpot(TM) 64-Bit Server VM (build 25.201-b09, mixed mode){code}
            Reporter: Sebastian Wiendl


After roughly 5-7 days of continued scraper operation (about 10 PLC tags, 100ms 
sampling rate), the scraper stops working with the following log 
output:{code}2019-12-12 18:08:29.569  WARN 23031 --- [nioEventLoopGroup-2-1] 
io.netty.channel.DefaultChannelPipeline  : An exceptionCaught() event was 
fired, and it reached at the tail of the pipeline. It usually means the last 
handler in the pipeline did not handle the exception.

io.netty.util.internal.OutOfDirectMemoryError: failed to allocate 16777216 
byte(s) of direct memory (used: 1845493760, max: 1860698112)
        at 
io.netty.util.internal.PlatformDependent.incrementMemoryCounter(PlatformDependent.java:726)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.PlatformDependent.allocateDirectNoCleaner(PlatformDependent.java:681)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PoolArena$DirectArena.allocateDirect(PoolArena.java:758) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena$DirectArena.newChunk(PoolArena.java:734) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocateNormal(PoolArena.java:245) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:215) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:147) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PooledByteBufAllocator.newDirectBuffer(PooledByteBufAllocator.java:342)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.directBuffer(AbstractByteBufAllocator.java:187)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.directBuffer(AbstractByteBufAllocator.java:178)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.ioBuffer(AbstractByteBufAllocator.java:139)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.DefaultMaxMessagesRecvByteBufAllocator$MaxMessageHandle.allocate(DefaultMaxMessagesRecvByteBufAllocator.java:114)
 ~[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:147)
 ~[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:700) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:635)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:552) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:514) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.SingleThreadEventExecutor$6.run(SingleThreadEventExecutor.java:1050)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74) 
[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at java.lang.Thread.run(Thread.java:748) [na:1.8.0_201]

2019-12-12 18:08:29.569  WARN 23031 --- [nioEventLoopGroup-2-1] 
io.netty.channel.DefaultChannelPipeline  : An exceptionCaught() event was 
fired, and it reached at the tail of the pipeline. It usually means the last 
handler in the pipeline did not handle the exception.

io.netty.util.internal.OutOfDirectMemoryError: failed to allocate 16777216 
byte(s) of direct memory (used: 1845493760, max: 1860698112)
        at 
io.netty.util.internal.PlatformDependent.incrementMemoryCounter(PlatformDependent.java:726)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.PlatformDependent.allocateDirectNoCleaner(PlatformDependent.java:681)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PoolArena$DirectArena.allocateDirect(PoolArena.java:758) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena$DirectArena.newChunk(PoolArena.java:734) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocateNormal(PoolArena.java:245) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:215) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:147) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PooledByteBufAllocator.newDirectBuffer(PooledByteBufAllocator.java:342)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.directBuffer(AbstractByteBufAllocator.java:187)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.directBuffer(AbstractByteBufAllocator.java:178)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.ioBuffer(AbstractByteBufAllocator.java:139)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.DefaultMaxMessagesRecvByteBufAllocator$MaxMessageHandle.allocate(DefaultMaxMessagesRecvByteBufAllocator.java:114)
 ~[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:147)
 ~[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:700) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:635)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:552) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:514) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.SingleThreadEventExecutor$6.run(SingleThreadEventExecutor.java:1050)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74) 
[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at java.lang.Thread.run(Thread.java:748) [na:1.8.0_201]

2019-12-12 18:08:29.570  WARN 23031 --- [nioEventLoopGroup-2-1] 
io.netty.channel.DefaultChannelPipeline  : An exceptionCaught() event was 
fired, and it reached at the tail of the pipeline. It usually means the last 
handler in the pipeline did not handle the exception.

io.netty.util.internal.OutOfDirectMemoryError: failed to allocate 16777216 
byte(s) of direct memory (used: 1845493760, max: 1860698112)
        at 
io.netty.util.internal.PlatformDependent.incrementMemoryCounter(PlatformDependent.java:726)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.PlatformDependent.allocateDirectNoCleaner(PlatformDependent.java:681)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PoolArena$DirectArena.allocateDirect(PoolArena.java:758) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena$DirectArena.newChunk(PoolArena.java:734) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocateNormal(PoolArena.java:245) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:215) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:147) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PooledByteBufAllocator.newDirectBuffer(PooledByteBufAllocator.java:342)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.directBuffer(AbstractByteBufAllocator.java:187)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.directBuffer(AbstractByteBufAllocator.java:178)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.ioBuffer(AbstractByteBufAllocator.java:139)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.DefaultMaxMessagesRecvByteBufAllocator$MaxMessageHandle.allocate(DefaultMaxMessagesRecvByteBufAllocator.java:114)
 ~[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:147)
 ~[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:700) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:635)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:552) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:514) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.SingleThreadEventExecutor$6.run(SingleThreadEventExecutor.java:1050)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74) 
[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at java.lang.Thread.run(Thread.java:748) [na:1.8.0_201]

2019-12-12 18:08:29.570  WARN 23031 --- [nioEventLoopGroup-2-1] 
io.netty.channel.DefaultChannelPipeline  : An exceptionCaught() event was 
fired, and it reached at the tail of the pipeline. It usually means the last 
handler in the pipeline did not handle the exception.

io.netty.util.internal.OutOfDirectMemoryError: failed to allocate 16777216 
byte(s) of direct memory (used: 1845493760, max: 1860698112)
        at 
io.netty.util.internal.PlatformDependent.incrementMemoryCounter(PlatformDependent.java:726)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.PlatformDependent.allocateDirectNoCleaner(PlatformDependent.java:681)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PoolArena$DirectArena.allocateDirect(PoolArena.java:758) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena$DirectArena.newChunk(PoolArena.java:734) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocateNormal(PoolArena.java:245) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:215) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:147) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PooledByteBufAllocator.newDirectBuffer(PooledByteBufAllocator.java:342)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.directBuffer(AbstractByteBufAllocator.java:187)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.directBuffer(AbstractByteBufAllocator.java:178)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.ioBuffer(AbstractByteBufAllocator.java:139)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.DefaultMaxMessagesRecvByteBufAllocator$MaxMessageHandle.allocate(DefaultMaxMessagesRecvByteBufAllocator.java:114)
 ~[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:147)
 ~[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:700) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:635)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:552) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:514) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.SingleThreadEventExecutor$6.run(SingleThreadEventExecutor.java:1050)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74) 
[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at java.lang.Thread.run(Thread.java:748) [na:1.8.0_201]

2019-12-12 18:08:29.570  WARN 23031 --- [nioEventLoopGroup-2-1] 
io.netty.channel.DefaultChannelPipeline  : An exceptionCaught() event was 
fired, and it reached at the tail of the pipeline. It usually means the last 
handler in the pipeline did not handle the exception.

io.netty.util.internal.OutOfDirectMemoryError: failed to allocate 16777216 
byte(s) of direct memory (used: 1845493760, max: 1860698112)
        at 
io.netty.util.internal.PlatformDependent.incrementMemoryCounter(PlatformDependent.java:726)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.PlatformDependent.allocateDirectNoCleaner(PlatformDependent.java:681)
 ~[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PoolArena$DirectArena.allocateDirect(PoolArena.java:758) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena$DirectArena.newChunk(PoolArena.java:734) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocateNormal(PoolArena.java:245) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:215) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.PoolArena.allocate(PoolArena.java:147) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.PooledByteBufAllocator.newDirectBuffer(PooledByteBufAllocator.java:342)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.directBuffer(AbstractByteBufAllocator.java:187)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.buffer.AbstractByteBufAllocator.buffer(AbstractByteBufAllocator.java:123)
 ~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.buffer.AbstractByteBuf.readBytes(AbstractByteBuf.java:886) 
~[netty-buffer-4.1.43.Final.jar!/:4.1.43.Final]
        at 
org.apache.plc4x.java.isoontcp.protocol.IsoOnTcpProtocol.decode(IsoOnTcpProtocol.java:100)
 ~[plc4j-protocol-iso-on-tcp-0.5.0.jar!/:0.5.0]
        at 
io.netty.handler.codec.ByteToMessageCodec$1.decode(ByteToMessageCodec.java:42) 
~[netty-codec-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.handler.codec.ByteToMessageDecoder.decodeRemovalReentryProtection(ByteToMessageDecoder.java:503)
 ~[netty-codec-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.handler.codec.ByteToMessageDecoder.callDecode(ByteToMessageDecoder.java:442)
 ~[netty-codec-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:281)
 ~[netty-codec-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
 ~[netty-codec-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:374)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:360)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:352)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1422)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:374)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:360)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:931)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:163)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:700) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:635)
 [netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:552) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:514) 
[netty-transport-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.SingleThreadEventExecutor$6.run(SingleThreadEventExecutor.java:1050)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74) 
[netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at 
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
 [netty-common-4.1.43.Final.jar!/:4.1.43.Final]
        at java.lang.Thread.run(Thread.java:748) [na:1.8.0_201]

2019-12-12 18:08:31.563  WARN 23031 --- [triggeredscraper-scheduling-thread-20] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:33.564  WARN 23031 --- [triggeredscraper-scheduling-thread-20] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:35.565  WARN 23031 --- [triggeredscraper-scheduling-thread-20] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:37.566  WARN 23031 --- [triggeredscraper-scheduling-thread-20] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:39.566  WARN 23031 --- [triggeredscraper-scheduling-thread-20] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:41.567  WARN 23031 --- [triggeredscraper-scheduling-thread-20] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:43.568  WARN 23031 --- [triggeredscraper-scheduling-thread-20] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:45.568  WARN 23031 --- [triggeredscraper-scheduling-thread-20] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:47.569  WARN 23031 --- [triggeredscraper-scheduling-thread-20] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:49.569  WARN 23031 --- [triggeredscraper-scheduling-thread-7] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG
2019-12-12 18:08:51.570  WARN 23031 --- [triggeredscraper-scheduling-thread-7] 
o.a.p.j.s.t.TriggeredScraperTask         : Exception during scraping of Job 
example, Connection-Alias S7: Error-message: null - for stack-trace change 
logging to DEBUG{code}



--
This message was sent by Atlassian Jira
(v8.3.4#803005)

Reply via email to