https://issues.apache.org/jira/browse/PLC4X-220?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17165505#comment-17165505
 ] 

Christofer Dutz commented on PLC4X-220:
---------------------------------------

Hi Steffano,

I think you might be using the connection pool the wrong way. Instead of 
getting a connection and keeping it, this will not make the pooling do it's 
magic. So please create an instance of the PooledPlcDriverManager in your main 
application and pass that in to the Pollers ... there inside the run method you 
use the driverManager to get a connection, build the request and execute it and 
then you give it back to the pool by closing the connection. The pooled driver 
manager will return the connection to the pool without closing it as soon as 
you call "close".

I did see a pattern of two subsequent requests being fired to the PLC where the 
plc only seems to respond to the first of the two.

Also something strange is that the last packet, which isn't responded to, on 
COTP protocol level always has a TPDU Number with "0x?F" ... so the last 4 bits 
are always one. But I would assume that's just a coincidence.

Could you please re-try with the modifications I suggested above?

 

Chris

 

> Connection die in multithreading
> --------------------------------
>
>                 Key: PLC4X-220
>                 URL: https://issues.apache.org/jira/browse/PLC4X-220
>             Project: Apache PLC4X
>          Issue Type: Bug
>          Components: Driver-S7
>    Affects Versions: 0.7.0
>            Reporter: Stefano Bossi
>            Priority: Major
>         Attachments: capture01.pcapng, capture02.pcapng
>
>
> Dear developers,
> I wrote a test application to show you the problem as requested.
> The test app fire a couple of thread which read a field in a DB (Siemens 1200 
> S7) continuously; the problem is that after some seconds one of the two 
> thread fire an untrappable exception and the software dies.
> Here is my code:
> ```java
> package it.fox;
> import org.apache.logging.log4j.LogManager;
> import org.apache.logging.log4j.Logger;
> import org.apache.plc4x.java.api.PlcConnection;
> import org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager;
> public class App {
>     private static final Logger logger = LogManager.getLogger(App.class);
>     public static void main(String[] args) {
>         try {
>             PlcConnection plcConnection = new 
> PooledPlcDriverManager().getConnection("s7://192.168.1.192?controller-type=S7_1200");
>             if (plcConnection.getMetadata().canRead() ) {
>                 Poller01 poller01 = new Poller01();
>                 poller01.start(plcConnection);
>                 Poller02 poller02 = new Poller02();
>                 poller02.start(plcConnection);
>             } else {
>                 logger.error("This connection doesn't support reading.");
>                 Thread.sleep(5000);
>             }
>         } catch (Exception exception) {
>             logger.error("Error connecting to the PLC", exception);
>         }
>     }
> }
> ```
> ```java
> package it.fox;
> import java.util.concurrent.TimeUnit;
> import org.apache.logging.log4j.LogManager;
> import org.apache.logging.log4j.Logger;
> import org.apache.plc4x.java.api.PlcConnection;
> import org.apache.plc4x.java.api.messages.PlcReadRequest;
> import org.apache.plc4x.java.api.messages.PlcReadResponse;
> public class Poller01 implements Runnable {
>     private static final Logger logger = LogManager.getLogger(Poller01.class);
>     private Thread thread;
>     private PlcConnection plcConnection;
>     
>     @Override
>     public void run() {
>         PlcReadRequest.Builder requestBuilder = 
> plcConnection.readRequestBuilder();
>         requestBuilder.addItem("data", "%DB1:262.0:INT");
>         PlcReadRequest readRequest = requestBuilder.build();
>         while(true){
>             try {
>                 PlcReadResponse response = readRequest.execute().get(5000, 
> TimeUnit.MILLISECONDS);
>                 if (response != null){
>                     logger.info("poller01 = {}", response.getPlcValue("data") 
> );
>                     Thread.sleep( (int) Math.floor(Math.random() * 100) );
>                 } else {
>                     logger.error("No response from PLC in reading polling 
> variable");
>                     break;
>                 }
>             } catch (Exception e) {
>                 logger.error("Poller01 Exception", e);
>             }
>         }
>     }
>     
>     /**
>      * Start the thread
>      */
>     public void start(PlcConnection plcConnection) {
>         this.plcConnection = plcConnection;
>         logger.info("Starting poller01 thread");
>         if (thread == null) {
>             thread = new Thread(this, "poller01");
>             thread.start();
>         }
>     }
> }
> ```
> ```java
> package it.fox;
> import java.util.concurrent.TimeUnit;
> import org.apache.logging.log4j.LogManager;
> import org.apache.logging.log4j.Logger;
> import org.apache.plc4x.java.api.PlcConnection;
> import org.apache.plc4x.java.api.messages.PlcReadRequest;
> import org.apache.plc4x.java.api.messages.PlcReadResponse;
> public class Poller02 implements Runnable{
>     
>     private static final Logger logger = LogManager.getLogger(Poller02.class);
>     private Thread thread;
>     private PlcConnection plcConnection;
>     @Override
>     public void run() {
>         PlcReadRequest.Builder requestBuilder = 
> plcConnection.readRequestBuilder();
>         requestBuilder.addItem("data", "%DB1:0.0:DINT");
>         PlcReadRequest readRequest = requestBuilder.build();
>         while(true){
>             try {
>                 PlcReadResponse response = readRequest.execute().get(5000, 
> TimeUnit.MILLISECONDS);
>                 if (response != null){
>                     logger.info("poller02 = {}", response.getPlcValue("data") 
> );
>                     Thread.sleep( (int) Math.floor(Math.random() * 500) );
>                 } else {
>                     logger.error("No response from PLC in reading polling 
> variable");
>                     break;
>                 }
>             } catch (Exception e) {
>                 logger.error("Poller01 Exception", e);
>             }
>         }
>     }
>     
>     /**
>      * Start the thread
>      */
>     public void start(PlcConnection plcConnection) {
>         this.plcConnection = plcConnection;
>         logger.info("Starting poller02 thread");
>         if (thread == null) {
>             thread = new Thread(this, "poller02");
>             thread.start();
>         }
>     }
> }
> ```
> The fired exception in the log is:
> ```
> [INFO ] 08:57:08.016 org.apache.plc4x.java.PlcDriverManager.<init>() - 
> Instantiating new PLC Driver Manager with class loader 
> jdk.internal.loader.ClassLoaders$AppClassLoader@55054057
> [INFO ] 08:57:08.019 org.apache.plc4x.java.PlcDriverManager.<init>() - 
> Registering available drivers...
> [INFO ] 08:57:08.023 org.apache.plc4x.java.PlcDriverManager.<init>() - 
> Registering driver for Protocol s7 (Siemens S7 (Basic))
> [DEBUG] 08:57:08.029 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager.getConnection()
>  - Try to borrow an object for url s7://192.168.1.192?controller-type=S7_1200
> [DEBUG] 08:57:08.032 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager.create() - 
> getting actual connection for s7://192.168.1.192?controller-type=S7_1200
> [DEBUG] 08:57:08.086 
> io.netty.util.internal.logging.InternalLoggerFactory.newDefaultFactory() - 
> Using SLF4J as the default logging framework
> [DEBUG] 08:57:08.090 io.netty.util.ResourceLeakDetector.<clinit>() - 
> -Dio.netty.leakDetection.level: simple
> [DEBUG] 08:57:08.090 io.netty.util.ResourceLeakDetector.<clinit>() - 
> -Dio.netty.leakDetection.targetRecords: 4
> [DEBUG] 08:57:08.094 
> io.netty.util.ResourceLeakDetectorFactory.newResourceLeakDetector() - Loaded 
> default ResourceLeakDetector: io.netty.util.ResourceLeakDetector@74f6c5d8
> [DEBUG] 08:57:08.105 io.netty.util.internal.PlatformDependent.isOsx0() - 
> Platform: MacOS
> [DEBUG] 08:57:08.107 
> io.netty.util.internal.PlatformDependent0.explicitNoUnsafeCause0() - 
> -Dio.netty.noUnsafe: false
> [DEBUG] 08:57:08.108 io.netty.util.internal.PlatformDependent0.javaVersion0() 
> - Java version: 13
> [DEBUG] 08:57:08.110 io.netty.util.internal.PlatformDependent0.<clinit>() - 
> sun.misc.Unsafe.theUnsafe: available
> [DEBUG] 08:57:08.111 io.netty.util.internal.PlatformDependent0.<clinit>() - 
> sun.misc.Unsafe.copyMemory: available
> [DEBUG] 08:57:08.111 io.netty.util.internal.PlatformDependent0.<clinit>() - 
> java.nio.Buffer.address: available
> [DEBUG] 08:57:08.112 io.netty.util.internal.PlatformDependent0.<clinit>() - 
> direct buffer constructor: unavailable
> java.lang.UnsupportedOperationException: Reflective setAccessible(true) 
> disabled
>       at 
> io.netty.util.internal.ReflectionUtil.trySetAccessible(ReflectionUtil.java:31)
>  ~[netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.util.internal.PlatformDependent0$4.run(PlatformDependent0.java:225) 
> ~[netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> java.security.AccessController.doPrivileged(AccessController.java:312) ~[?:?]
>       at 
> io.netty.util.internal.PlatformDependent0.<clinit>(PlatformDependent0.java:219)
>  [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.util.internal.PlatformDependent.isAndroid(PlatformDependent.java:289)
>  [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.util.internal.PlatformDependent.<clinit>(PlatformDependent.java:92) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:109) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:218) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:197) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:179) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:163) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:122) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> org.apache.plc4x.java.spi.connection.DefaultNettyPlcConnection.<clinit>(DefaultNettyPlcConnection.java:49)
>  [plc4j-spi-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.spi.connection.GeneratedDriverBase.getConnection(GeneratedDriverBase.java:138)
>  [plc4j-spi-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:73)
>  [plc4j-api-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager.access$201(PooledPlcDriverManager.java:37)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager$1.create(PooledPlcDriverManager.java:89)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager$1.create(PooledPlcDriverManager.java:82)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at 
> org.apache.commons.pool2.BaseKeyedPooledObjectFactory.makeObject(BaseKeyedPooledObjectFactory.java:62)
>  [commons-pool2-2.8.0.jar:2.8.0]
>       at 
> org.apache.commons.pool2.impl.GenericKeyedObjectPool.create(GenericKeyedObjectPool.java:1051)
>  [commons-pool2-2.8.0.jar:2.8.0]
>       at 
> org.apache.commons.pool2.impl.GenericKeyedObjectPool.borrowObject(GenericKeyedObjectPool.java:347)
>  [commons-pool2-2.8.0.jar:2.8.0]
>       at 
> org.apache.commons.pool2.impl.GenericKeyedObjectPool.borrowObject(GenericKeyedObjectPool.java:270)
>  [commons-pool2-2.8.0.jar:2.8.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager.getConnection(PooledPlcDriverManager.java:115)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager.getConnection(PooledPlcDriverManager.java:100)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at it.fox.App.main(App.java:14) [main/:?]
> [DEBUG] 08:57:08.123 io.netty.util.internal.PlatformDependent0.<clinit>() - 
> java.nio.Bits.unaligned: available, true
> [DEBUG] 08:57:08.125 io.netty.util.internal.PlatformDependent0.<clinit>() - 
> jdk.internal.misc.Unsafe.allocateUninitializedArray(int): unavailable
> java.lang.IllegalAccessException: class 
> io.netty.util.internal.PlatformDependent0$6 cannot access class 
> jdk.internal.misc.Unsafe (in module java.base) because module java.base does 
> not export jdk.internal.misc to unnamed module @421e361
>       at 
> jdk.internal.reflect.Reflection.newIllegalAccessException(Reflection.java:376)
>  ~[?:?]
>       at 
> java.lang.reflect.AccessibleObject.checkAccess(AccessibleObject.java:642) 
> ~[?:?]
>       at java.lang.reflect.Method.invoke(Method.java:559) ~[?:?]
>       at 
> io.netty.util.internal.PlatformDependent0$6.run(PlatformDependent0.java:335) 
> ~[netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> java.security.AccessController.doPrivileged(AccessController.java:312) ~[?:?]
>       at 
> io.netty.util.internal.PlatformDependent0.<clinit>(PlatformDependent0.java:326)
>  [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.util.internal.PlatformDependent.isAndroid(PlatformDependent.java:289)
>  [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.util.internal.PlatformDependent.<clinit>(PlatformDependent.java:92) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:109) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:218) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:197) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:179) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:163) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.util.HashedWheelTimer.<init>(HashedWheelTimer.java:122) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> org.apache.plc4x.java.spi.connection.DefaultNettyPlcConnection.<clinit>(DefaultNettyPlcConnection.java:49)
>  [plc4j-spi-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.spi.connection.GeneratedDriverBase.getConnection(GeneratedDriverBase.java:138)
>  [plc4j-spi-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:73)
>  [plc4j-api-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager.access$201(PooledPlcDriverManager.java:37)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager$1.create(PooledPlcDriverManager.java:89)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager$1.create(PooledPlcDriverManager.java:82)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at 
> org.apache.commons.pool2.BaseKeyedPooledObjectFactory.makeObject(BaseKeyedPooledObjectFactory.java:62)
>  [commons-pool2-2.8.0.jar:2.8.0]
>       at 
> org.apache.commons.pool2.impl.GenericKeyedObjectPool.create(GenericKeyedObjectPool.java:1051)
>  [commons-pool2-2.8.0.jar:2.8.0]
>       at 
> org.apache.commons.pool2.impl.GenericKeyedObjectPool.borrowObject(GenericKeyedObjectPool.java:347)
>  [commons-pool2-2.8.0.jar:2.8.0]
>       at 
> org.apache.commons.pool2.impl.GenericKeyedObjectPool.borrowObject(GenericKeyedObjectPool.java:270)
>  [commons-pool2-2.8.0.jar:2.8.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager.getConnection(PooledPlcDriverManager.java:115)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcDriverManager.getConnection(PooledPlcDriverManager.java:100)
>  [plc4j-connection-pool-0.7.0.jar:0.7.0]
>       at it.fox.App.main(App.java:14) [main/:?]
> [DEBUG] 08:57:08.126 io.netty.util.internal.PlatformDependent0.<clinit>() - 
> java.nio.DirectByteBuffer.<init>(long, int): unavailable
> [DEBUG] 08:57:08.126 
> io.netty.util.internal.PlatformDependent.unsafeUnavailabilityCause0() - 
> sun.misc.Unsafe: available
> [DEBUG] 08:57:08.127 
> io.netty.util.internal.PlatformDependent.maxDirectMemory0() - 
> maxDirectMemory: 4294967296 bytes (maybe)
> [DEBUG] 08:57:08.128 io.netty.util.internal.PlatformDependent.tmpdir0() - 
> -Dio.netty.tmpdir: /var/folders/p1/lb5grfpn3tncxdtrptqq9fw40000gp/T 
> (java.io.tmpdir)
> [DEBUG] 08:57:08.128 io.netty.util.internal.PlatformDependent.bitMode0() - 
> -Dio.netty.bitMode: 64 (sun.arch.data.model)
> [DEBUG] 08:57:08.130 io.netty.util.internal.PlatformDependent.<clinit>() - 
> -Dio.netty.maxDirectMemory: -1 bytes
> [DEBUG] 08:57:08.131 io.netty.util.internal.PlatformDependent.<clinit>() - 
> -Dio.netty.uninitializedArrayAllocationThreshold: -1
> [DEBUG] 08:57:08.133 io.netty.util.internal.CleanerJava9.<clinit>() - 
> java.nio.ByteBuffer.cleaner(): available
> [DEBUG] 08:57:08.133 io.netty.util.internal.PlatformDependent.<clinit>() - 
> -Dio.netty.noPreferDirect: false
> [DEBUG] 08:57:08.141 io.netty.util.internal.PlatformDependent.<clinit>() - 
> org.jctools-core.MpscChunkedArrayQueue: available
> [DEBUG] 08:57:08.168 io.netty.channel.MultithreadEventLoopGroup.<clinit>() - 
> -Dio.netty.eventLoopThreads: 16
> [DEBUG] 08:57:08.178 io.netty.util.internal.InternalThreadLocalMap.<clinit>() 
> - -Dio.netty.threadLocalMap.stringBuilder.initialSize: 1024
> [DEBUG] 08:57:08.179 io.netty.util.internal.InternalThreadLocalMap.<clinit>() 
> - -Dio.netty.threadLocalMap.stringBuilder.maxSize: 4096
> [DEBUG] 08:57:08.183 io.netty.channel.nio.NioEventLoop.<clinit>() - 
> -Dio.netty.noKeySetOptimization: false
> [DEBUG] 08:57:08.183 io.netty.channel.nio.NioEventLoop.<clinit>() - 
> -Dio.netty.selectorAutoRebuildThreshold: 512
> [INFO ] 08:57:08.192 
> org.apache.plc4x.java.transport.tcp.TcpChannelFactory.configureBootstrap() - 
> Configuring Bootstrap with Configuration{local-rack=1, local-slot=1, 
> remote-rack=0, remot-slot=0, pduSize=1024, maxAmqCaller=8, maxAmqCallee=8, 
> controllerType='S7_1200'}
> [DEBUG] 08:57:08.205 io.netty.channel.DefaultChannelId.<clinit>() - 
> -Dio.netty.processId: 48162 (auto-detected)
> [DEBUG] 08:57:08.207 io.netty.util.NetUtil.<clinit>() - 
> -Djava.net.preferIPv4Stack: false
> [DEBUG] 08:57:08.208 io.netty.util.NetUtil.<clinit>() - 
> -Djava.net.preferIPv6Addresses: false
> [DEBUG] 08:57:08.211 io.netty.util.NetUtil.<clinit>() - Loopback interface: 
> lo0 (lo0, 0:0:0:0:0:0:0:1%lo0)
> [DEBUG] 08:57:08.212 io.netty.util.NetUtil.run() - Failed to get SOMAXCONN 
> from sysctl and file /proc/sys/net/core/somaxconn. Default: 128
> [DEBUG] 08:57:08.214 io.netty.channel.DefaultChannelId.<clinit>() - 
> -Dio.netty.machineId: 68:5b:35:ff:fe:98:95:7f (auto-detected)
> [DEBUG] 08:57:08.237 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.numHeapArenas: 16
> [DEBUG] 08:57:08.237 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.numDirectArenas: 16
> [DEBUG] 08:57:08.237 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.pageSize: 8192
> [DEBUG] 08:57:08.238 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.maxOrder: 11
> [DEBUG] 08:57:08.238 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.chunkSize: 16777216
> [DEBUG] 08:57:08.239 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.tinyCacheSize: 512
> [DEBUG] 08:57:08.239 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.smallCacheSize: 256
> [DEBUG] 08:57:08.239 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.normalCacheSize: 64
> [DEBUG] 08:57:08.240 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.maxCachedBufferCapacity: 32768
> [DEBUG] 08:57:08.240 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.cacheTrimInterval: 8192
> [DEBUG] 08:57:08.240 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.cacheTrimIntervalMillis: 0
> [DEBUG] 08:57:08.241 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.useCacheForAllThreads: true
> [DEBUG] 08:57:08.241 io.netty.buffer.PooledByteBufAllocator.<clinit>() - 
> -Dio.netty.allocator.maxCachedByteBuffersPerChunk: 1023
> [DEBUG] 08:57:08.247 io.netty.buffer.ByteBufUtil.<clinit>() - 
> -Dio.netty.allocator.type: pooled
> [DEBUG] 08:57:08.247 io.netty.buffer.ByteBufUtil.<clinit>() - 
> -Dio.netty.threadLocalDirectBufferSize: 0
> [DEBUG] 08:57:08.247 io.netty.buffer.ByteBufUtil.<clinit>() - 
> -Dio.netty.maxThreadLocalCharBufferSize: 16384
> [DEBUG] 08:57:08.301 
> org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic.onConnect() - 
> Sending COTP Connection Request
> [DEBUG] 08:57:08.323 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketConnectionRequest[parameters={COTPParameterCalledTsap[tsapId=256],COTPParameterCallingTsap[tsapId=785],COTPParameterTpduSize[tpduSize=SIZE_1024]},payload=<null>,destinationReference=0,sourceReference=15,protocolClass=CLASS_0]]
> [DEBUG] 08:57:08.328 io.netty.util.Recycler.<clinit>() - 
> -Dio.netty.recycler.maxCapacityPerThread: 4096
> [DEBUG] 08:57:08.328 io.netty.util.Recycler.<clinit>() - 
> -Dio.netty.recycler.maxSharedCapacityFactor: 2
> [DEBUG] 08:57:08.328 io.netty.util.Recycler.<clinit>() - 
> -Dio.netty.recycler.linkCapacity: 16
> [DEBUG] 08:57:08.328 io.netty.util.Recycler.<clinit>() - 
> -Dio.netty.recycler.ratio: 8
> [DEBUG] 08:57:08.336 io.netty.buffer.AbstractByteBuf.<clinit>() - 
> -Dio.netty.buffer.checkAccessible: true
> [DEBUG] 08:57:08.336 io.netty.buffer.AbstractByteBuf.<clinit>() - 
> -Dio.netty.buffer.checkBounds: true
> [DEBUG] 08:57:08.337 
> io.netty.util.ResourceLeakDetectorFactory.newResourceLeakDetector() - Loaded 
> default ResourceLeakDetector: io.netty.util.ResourceLeakDetector@44c6a869
> [DEBUG] 08:57:08.355 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketConnectionRequest[parameters={COTPParameterCalledTsap[tsapId=256],COTPParameterCallingTsap[tsapId=785],COTPParameterTpduSize[tpduSize=SIZE_1024]},payload=<null>,destinationReference=0,sourceReference=15,protocolClass=CLASS_0]]
>  as data 0300001611e00000000f00c2020100c1020311c0010a
> [DEBUG] 08:57:08.383 
> org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic.lambda$onConnect$9()
>  - Got COTP Connection Response
> [DEBUG] 08:57:08.384 
> org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic.lambda$onConnect$9()
>  - Sending S7 Connection Request
> [DEBUG] 08:57:08.386 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=0,parameter=S7ParameterSetupCommunication[maxAmqCaller=8,maxAmqCallee=8,pduLength=1008],payload=<null>],eot=true,tpduRef=1]]
> [DEBUG] 08:57:08.389 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=0,parameter=S7ParameterSetupCommunication[maxAmqCaller=8,maxAmqCallee=8,pduLength=1008],payload=<null>],eot=true,tpduRef=1]]
>  as data 0300001902f08132010000000000080000f0000008000803f0
> [DEBUG] 08:57:08.405 
> org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic.lambda$onConnect$8()
>  - Got S7 Connection Response
> [DEBUG] 08:57:08.405 
> org.apache.plc4x.java.utils.connectionpool.PooledPlcConnectionFactory.wrap() 
> - Wrapping connection 
> org.apache.plc4x.java.spi.connection.DefaultNettyPlcConnection@299321e2
> [INFO ] 08:57:08.409 it.fox.Poller01.start() - Starting poller01 thread
> [INFO ] 08:57:08.410 it.fox.Poller02.start() - Starting poller02 thread
> [DEBUG] 08:57:08.424 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=11,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=11]]
> [DEBUG] 08:57:08.427 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=11,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=11]]
>  as data 0300001f02f08b32010000000b000e00000401120a10050001000184000830
> [INFO ] 08:57:08.457 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:08.458 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=10,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=10]]
> [DEBUG] 08:57:08.459 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=10,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=10]]
>  as data 0300001f02f08a32010000000a000e00000401120a10070001000184000000
> [INFO ] 08:57:08.475 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:08.484 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=12,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=12]]
> [DEBUG] 08:57:08.485 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=12,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=12]]
>  as data 0300001f02f08c32010000000c000e00000401120a10050001000184000830
> [INFO ] 08:57:08.505 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:08.537 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=13,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=13]]
> [DEBUG] 08:57:08.538 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=13,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=13]]
>  as data 0300001f02f08d32010000000d000e00000401120a10050001000184000830
> [INFO ] 08:57:08.555 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:08.642 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=14,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=14]]
> [DEBUG] 08:57:08.643 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=14,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=14]]
>  as data 0300001f02f08e32010000000e000e00000401120a10050001000184000830
> [INFO ] 08:57:08.664 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:08.717 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=15,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=15]]
> [DEBUG] 08:57:08.718 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=15,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=15]]
>  as data 0300001f02f08f32010000000f000e00000401120a10050001000184000830
> [INFO ] 08:57:08.734 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:08.805 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=16,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=16]]
> [DEBUG] 08:57:08.806 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=16,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=16]]
>  as data 0300001f02f090320100000010000e00000401120a10050001000184000830
> [INFO ] 08:57:08.825 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:08.867 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=17,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=17]]
> [DEBUG] 08:57:08.868 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=17,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=17]]
>  as data 0300001f02f091320100000011000e00000401120a10070001000184000000
> [INFO ] 08:57:08.885 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:08.911 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=18,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=18]]
> [DEBUG] 08:57:08.912 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=18,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=18]]
>  as data 0300001f02f092320100000012000e00000401120a10050001000184000830
> [INFO ] 08:57:08.930 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.009 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=19,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=19]]
> [DEBUG] 08:57:09.011 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=19,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=19]]
>  as data 0300001f02f093320100000013000e00000401120a10050001000184000830
> [INFO ] 08:57:09.040 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.116 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=20,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=20]]
> [DEBUG] 08:57:09.117 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=20,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=20]]
>  as data 0300001f02f094320100000014000e00000401120a10050001000184000830
> [INFO ] 08:57:09.139 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.196 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=21,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=21]]
> [DEBUG] 08:57:09.197 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=21,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=21]]
>  as data 0300001f02f095320100000015000e00000401120a10070001000184000000
> [INFO ] 08:57:09.215 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:09.215 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=22,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=22]]
> [DEBUG] 08:57:09.215 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=22,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=22]]
>  as data 0300001f02f096320100000016000e00000401120a10050001000184000830
> [INFO ] 08:57:09.235 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.249 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=23,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=23]]
> [DEBUG] 08:57:09.250 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=23,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=23]]
>  as data 0300001f02f097320100000017000e00000401120a10070001000184000000
> [INFO ] 08:57:09.274 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:09.275 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=24,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=24]]
> [DEBUG] 08:57:09.276 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=24,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=24]]
>  as data 0300001f02f098320100000018000e00000401120a10050001000184000830
> [INFO ] 08:57:09.295 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.298 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=25,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=25]]
> [DEBUG] 08:57:09.299 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=25,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=25]]
>  as data 0300001f02f099320100000019000e00000401120a10050001000184000830
> [INFO ] 08:57:09.315 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.334 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=26,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=26]]
> [DEBUG] 08:57:09.334 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=26,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=26]]
>  as data 0300001f02f09a32010000001a000e00000401120a10070001000184000000
> [INFO ] 08:57:09.354 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:09.371 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=27,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=27]]
> [DEBUG] 08:57:09.371 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=27,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=27]]
>  as data 0300001f02f09b32010000001b000e00000401120a10050001000184000830
> [INFO ] 08:57:09.390 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.402 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=28,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=28]]
> [DEBUG] 08:57:09.403 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=28,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=28]]
>  as data 0300001f02f09c32010000001c000e00000401120a10070001000184000000
> [INFO ] 08:57:09.419 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:09.454 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=29,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=29]]
> [DEBUG] 08:57:09.455 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=29,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=29]]
>  as data 0300001f02f09d32010000001d000e00000401120a10050001000184000830
> [INFO ] 08:57:09.475 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.533 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=30,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=30]]
> [DEBUG] 08:57:09.533 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=30,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=30]]
>  as data 0300001f02f09e32010000001e000e00000401120a10050001000184000830
> [INFO ] 08:57:09.554 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.602 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=31,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=31]]
> [DEBUG] 08:57:09.602 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=31,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=31]]
>  as data 0300001f02f09f32010000001f000e00000401120a10070001000184000000
> [INFO ] 08:57:09.620 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:09.647 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=32,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=32]]
> [DEBUG] 08:57:09.648 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=32,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=32]]
>  as data 0300001f02f0a0320100000020000e00000401120a10050001000184000830
> [INFO ] 08:57:09.674 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.674 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=33,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=33]]
> [DEBUG] 08:57:09.675 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=33,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=33]]
>  as data 0300001f02f0a1320100000021000e00000401120a10070001000184000000
> [INFO ] 08:57:09.694 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:09.728 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=34,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=34]]
> [DEBUG] 08:57:09.729 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=34,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=34]]
>  as data 0300001f02f0a2320100000022000e00000401120a10050001000184000830
> [INFO ] 08:57:09.749 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.758 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=35,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=35]]
> [DEBUG] 08:57:09.759 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=35,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=35]]
>  as data 0300001f02f0a3320100000023000e00000401120a10070001000184000000
> [INFO ] 08:57:09.775 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:09.833 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=36,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=36]]
> [DEBUG] 08:57:09.833 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=36,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=36]]
>  as data 0300001f02f0a4320100000024000e00000401120a10050001000184000830
> [INFO ] 08:57:09.854 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:09.951 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=37,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=37]]
> [DEBUG] 08:57:09.951 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=37,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=37]]
>  as data 0300001f02f0a5320100000025000e00000401120a10050001000184000830
> [INFO ] 08:57:09.975 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.042 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=38,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=38]]
> [DEBUG] 08:57:10.043 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=38,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=38]]
>  as data 0300001f02f0a6320100000026000e00000401120a10070001000184000000
> [INFO ] 08:57:10.064 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:10.065 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=39,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=39]]
> [DEBUG] 08:57:10.065 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=39,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=39]]
>  as data 0300001f02f0a7320100000027000e00000401120a10050001000184000830
> [INFO ] 08:57:10.085 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.179 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=40,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=40]]
> [DEBUG] 08:57:10.180 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=40,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=40]]
>  as data 0300001f02f0a8320100000028000e00000401120a10050001000184000830
> [INFO ] 08:57:10.200 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.228 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=41,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=41]]
> [DEBUG] 08:57:10.229 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=41,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=41]]
>  as data 0300001f02f0a9320100000029000e00000401120a10070001000184000000
> [INFO ] 08:57:10.249 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:10.296 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=42,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=42]]
> [DEBUG] 08:57:10.297 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=42,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=42]]
>  as data 0300001f02f0aa32010000002a000e00000401120a10050001000184000830
> [INFO ] 08:57:10.315 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.397 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=43,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=43]]
> [DEBUG] 08:57:10.398 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=43,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=43]]
>  as data 0300001f02f0ab32010000002b000e00000401120a10050001000184000830
> [INFO ] 08:57:10.414 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.435 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=44,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=44]]
> [DEBUG] 08:57:10.435 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=44,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=44]]
>  as data 0300001f02f0ac32010000002c000e00000401120a10050001000184000830
> [INFO ] 08:57:10.455 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.529 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=45,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=45]]
> [DEBUG] 08:57:10.529 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=45,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=45]]
>  as data 0300001f02f0ad32010000002d000e00000401120a10050001000184000830
> [INFO ] 08:57:10.549 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.622 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=46,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=46]]
> [DEBUG] 08:57:10.622 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=46,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=46]]
>  as data 0300001f02f0ae32010000002e000e00000401120a10070001000184000000
> [INFO ] 08:57:10.640 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:10.647 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=47,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=47]]
> [DEBUG] 08:57:10.648 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=47,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=47]]
>  as data 0300001f02f0af32010000002f000e00000401120a10050001000184000830
> [INFO ] 08:57:10.674 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.732 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=48,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=48]]
> [DEBUG] 08:57:10.733 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=48,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=48]]
>  as data 0300001f02f0b0320100000030000e00000401120a10050001000184000830
> [INFO ] 08:57:10.754 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.778 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=49,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=49]]
> [DEBUG] 08:57:10.778 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=49,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=49]]
>  as data 0300001f02f0b1320100000031000e00000401120a10050001000184000830
> [INFO ] 08:57:10.794 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:10.794 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=50,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=50]]
> [DEBUG] 08:57:10.795 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=50,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=50]]
>  as data 0300001f02f0b2320100000032000e00000401120a10070001000184000000
> [INFO ] 08:57:10.814 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:10.895 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=51,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=51]]
> [DEBUG] 08:57:10.896 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=51,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=51]]
>  as data 0300001f02f0b3320100000033000e00000401120a10050001000184000830
> [INFO ] 08:57:10.918 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.000 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=52,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=52]]
> [DEBUG] 08:57:11.001 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=52,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=52]]
>  as data 0300001f02f0b4320100000034000e00000401120a10070001000184000000
> [INFO ] 08:57:11.019 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:11.020 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=53,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=53]]
> [DEBUG] 08:57:11.020 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=53,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=53]]
>  as data 0300001f02f0b5320100000035000e00000401120a10050001000184000830
> [INFO ] 08:57:11.039 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.098 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=54,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=54]]
> [DEBUG] 08:57:11.099 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=54,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=54]]
>  as data 0300001f02f0b6320100000036000e00000401120a10050001000184000830
> [INFO ] 08:57:11.119 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.120 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=55,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=55]]
> [DEBUG] 08:57:11.121 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=55,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=55]]
>  as data 0300001f02f0b7320100000037000e00000401120a10050001000184000830
> [INFO ] 08:57:11.139 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.198 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=56,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=56]]
> [DEBUG] 08:57:11.198 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=56,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=56]]
>  as data 0300001f02f0b8320100000038000e00000401120a10050001000184000830
> [INFO ] 08:57:11.215 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.259 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=57,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=57]]
> [DEBUG] 08:57:11.260 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=57,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=57]]
>  as data 0300001f02f0b9320100000039000e00000401120a10070001000184000000
> [INFO ] 08:57:11.280 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:11.291 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=58,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=58]]
> [DEBUG] 08:57:11.292 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=58,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=58]]
>  as data 0300001f02f0ba32010000003a000e00000401120a10050001000184000830
> [INFO ] 08:57:11.310 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.409 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=59,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=59]]
> [DEBUG] 08:57:11.409 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=59,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=59]]
>  as data 0300001f02f0bb32010000003b000e00000401120a10050001000184000830
> [INFO ] 08:57:11.429 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.532 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=60,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=60]]
> [DEBUG] 08:57:11.532 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=60,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=60]]
>  as data 0300001f02f0bc32010000003c000e00000401120a10050001000184000830
> [INFO ] 08:57:11.553 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.589 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=61,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=61]]
> [DEBUG] 08:57:11.590 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=61,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=61]]
>  as data 0300001f02f0bd32010000003d000e00000401120a10050001000184000830
> [INFO ] 08:57:11.609 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.633 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=62,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=62]]
> [DEBUG] 08:57:11.634 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=62,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=62]]
>  as data 0300001f02f0be32010000003e000e00000401120a10050001000184000830
> [INFO ] 08:57:11.654 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.705 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=63,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=63]]
> [DEBUG] 08:57:11.705 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=63,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=63]]
>  as data 0300001f02f0bf32010000003f000e00000401120a10050001000184000830
> [INFO ] 08:57:11.734 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.734 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=64,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=64]]
> [DEBUG] 08:57:11.735 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=64,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=64]]
>  as data 0300001f02f0c0320100000040000e00000401120a10070001000184000000
> [INFO ] 08:57:11.784 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:11.784 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=65,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=65]]
> [DEBUG] 08:57:11.785 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=65,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=65]]
>  as data 0300001f02f0c1320100000041000e00000401120a10050001000184000830
> [INFO ] 08:57:11.804 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.880 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=66,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=66]]
> [DEBUG] 08:57:11.881 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=66,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=66]]
>  as data 0300001f02f0c2320100000042000e00000401120a10050001000184000830
> [INFO ] 08:57:11.904 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.906 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=67,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=67]]
> [DEBUG] 08:57:11.906 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=67,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=67]]
>  as data 0300001f02f0c3320100000043000e00000401120a10050001000184000830
> [INFO ] 08:57:11.924 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:11.952 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=68,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=68]]
> [DEBUG] 08:57:11.953 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=68,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=68]]
>  as data 0300001f02f0c4320100000044000e00000401120a10070001000184000000
> [INFO ] 08:57:11.969 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:11.969 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=69,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=69]]
> [DEBUG] 08:57:11.970 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=69,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=69]]
>  as data 0300001f02f0c5320100000045000e00000401120a10050001000184000830
> [INFO ] 08:57:11.989 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.034 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=70,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=70]]
> [DEBUG] 08:57:12.035 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=70,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=70]]
>  as data 0300001f02f0c6320100000046000e00000401120a10050001000184000830
> [INFO ] 08:57:12.054 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.132 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=71,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=71]]
> [DEBUG] 08:57:12.132 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=71,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=71]]
>  as data 0300001f02f0c7320100000047000e00000401120a10050001000184000830
> [INFO ] 08:57:12.154 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.189 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=72,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=72]]
> [DEBUG] 08:57:12.190 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=72,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=72]]
>  as data 0300001f02f0c8320100000048000e00000401120a10070001000184000000
> [INFO ] 08:57:12.209 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:12.256 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=73,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=73]]
> [DEBUG] 08:57:12.257 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=73,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=73]]
>  as data 0300001f02f0c9320100000049000e00000401120a10050001000184000830
> [INFO ] 08:57:12.274 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.292 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=74,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=74]]
> [DEBUG] 08:57:12.292 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=74,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=74]]
>  as data 0300001f02f0ca32010000004a000e00000401120a10050001000184000830
> [INFO ] 08:57:12.309 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.368 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=75,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=75]]
> [DEBUG] 08:57:12.369 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=75,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=75]]
>  as data 0300001f02f0cb32010000004b000e00000401120a10050001000184000830
> [INFO ] 08:57:12.389 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.430 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=76,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=76]]
> [DEBUG] 08:57:12.431 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=76,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=76]]
>  as data 0300001f02f0cc32010000004c000e00000401120a10050001000184000830
> [INFO ] 08:57:12.454 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.460 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=77,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=77]]
> [DEBUG] 08:57:12.460 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=77,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=77]]
>  as data 0300001f02f0cd32010000004d000e00000401120a10050001000184000830
> [INFO ] 08:57:12.479 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.490 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=78,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=78]]
> [DEBUG] 08:57:12.491 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=78,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=78]]
>  as data 0300001f02f0ce32010000004e000e00000401120a10050001000184000830
> [INFO ] 08:57:12.509 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.597 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=79,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=79]]
> [DEBUG] 08:57:12.598 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=79,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=79]]
>  as data 0300001f02f0cf32010000004f000e00000401120a10050001000184000830
> [INFO ] 08:57:12.614 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.648 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=80,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=80]]
> [DEBUG] 08:57:12.649 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=80,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=80]]
>  as data 0300001f02f0d0320100000050000e00000401120a10070001000184000000
> [INFO ] 08:57:12.674 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:12.691 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=81,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=81]]
> [DEBUG] 08:57:12.691 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=81,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=81]]
>  as data 0300001f02f0d1320100000051000e00000401120a10050001000184000830
> [INFO ] 08:57:12.709 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.737 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=82,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=82]]
> [DEBUG] 08:57:12.737 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=82,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=82]]
>  as data 0300001f02f0d2320100000052000e00000401120a10050001000184000830
> [INFO ] 08:57:12.754 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.767 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=83,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=83]]
> [DEBUG] 08:57:12.767 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=83,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=83]]
>  as data 0300001f02f0d3320100000053000e00000401120a10050001000184000830
> [INFO ] 08:57:12.784 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.806 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=84,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=84]]
> [DEBUG] 08:57:12.807 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=84,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=84]]
>  as data 0300001f02f0d4320100000054000e00000401120a10050001000184000830
> [INFO ] 08:57:12.824 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.851 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=85,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=85]]
> [DEBUG] 08:57:12.852 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=85,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=85]]
>  as data 0300001f02f0d5320100000055000e00000401120a10050001000184000830
> [INFO ] 08:57:12.870 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.941 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=86,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=86]]
> [DEBUG] 08:57:12.941 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=86,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=86]]
>  as data 0300001f02f0d6320100000056000e00000401120a10050001000184000830
> [INFO ] 08:57:12.963 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:12.978 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=87,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=87]]
> [DEBUG] 08:57:12.978 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=87,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=87]]
>  as data 0300001f02f0d7320100000057000e00000401120a10050001000184000830
> [INFO ] 08:57:12.995 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:13.049 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=88,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=88]]
> [DEBUG] 08:57:13.049 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=88,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=88]]
>  as data 0300001f02f0d8320100000058000e00000401120a10050001000184000830
> [INFO ] 08:57:13.069 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:13.106 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=89,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=89]]
> [DEBUG] 08:57:13.107 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=89,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=89]]
>  as data 0300001f02f0d9320100000059000e00000401120a10070001000184000000
> [INFO ] 08:57:13.124 it.fox.Poller02.run() - poller02 = 12139
> [DEBUG] 08:57:13.125 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=90,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=90]]
> [DEBUG] 08:57:13.125 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=90,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=90]]
>  as data 0300001f02f0da32010000005a000e00000401120a10050001000184000830
> [INFO ] 08:57:13.144 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:13.148 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=91,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=91]]
> [DEBUG] 08:57:13.148 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=91,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=91]]
>  as data 0300001f02f0db32010000005b000e00000401120a10050001000184000830
> [INFO ] 08:57:13.173 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:13.264 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=92,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=92]]
> [DEBUG] 08:57:13.264 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=92,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=92]]
>  as data 0300001f02f0dc32010000005c000e00000401120a10050001000184000830
> [INFO ] 08:57:13.284 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:13.320 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=93,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=93]]
> [DEBUG] 08:57:13.321 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=93,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=93]]
>  as data 0300001f02f0dd32010000005d000e00000401120a10050001000184000830
> [INFO ] 08:57:13.339 it.fox.Poller01.run() - poller01 = 7
> [DEBUG] 08:57:13.374 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=94,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=94]]
> [DEBUG] 08:57:13.374 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=94,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=DINT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=0,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=94]]
>  as data 0300001f02f0de32010000005e000e00000401120a10070001000184000000
> [DEBUG] 08:57:13.375 org.apache.plc4x.java.spi.Plc4xNettyWrapper.encode() - 
> Forwarding request to plc 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=95,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=95]]
> [DEBUG] 08:57:13.375 
> org.apache.plc4x.java.spi.GeneratedDriverByteToMessageCodec.encode() - 
> Sending bytes to PLC for message 
> TPKTPacket[payload=COTPPacketData[parameters=<null>,payload=S7MessageRequest[tpduReference=95,parameter=S7ParameterReadVarRequest[items={S7VarRequestParameterItemAddress[address=S7AddressAny[transportSize=INT,numberOfElements=1,dbNumber=1,area=DATA_BLOCKS,byteAddress=262,bitAddress=0]]}],payload=<null>],eot=true,tpduRef=95]]
>  as data 0300001f02f0df32010000005f000e00000401120a10050001000184000830
> [INFO ] 08:57:13.399 it.fox.Poller02.run() - poller02 = 12139
> [WARN ] 08:57:13.404 
> io.netty.channel.DefaultChannelPipeline.onUnhandledInboundException() - An 
> exceptionCaught() event was fired, and it reached at the tail of the 
> pipeline. It usually means the last handler in the pipeline did not handle 
> the exception.
> java.net.SocketException: Connection reset
>       at 
> sun.nio.ch.SocketChannelImpl.throwConnectionReset(SocketChannelImpl.java:345) 
> ~[?:?]
>       at sun.nio.ch.SocketChannelImpl.read(SocketChannelImpl.java:376) ~[?:?]
>       at io.netty.buffer.PooledByteBuf.setBytes(PooledByteBuf.java:253) 
> ~[netty-buffer-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.buffer.AbstractByteBuf.writeBytes(AbstractByteBuf.java:1133) 
> ~[netty-buffer-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.channel.socket.nio.NioSocketChannel.doReadBytes(NioSocketChannel.java:350)
>  ~[netty-transport-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:148)
>  [netty-transport-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:714) 
> [netty-transport-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:650)
>  [netty-transport-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:576) 
> [netty-transport-4.1.47.Final.jar:4.1.47.Final]
>       at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:493) 
> [netty-transport-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.util.concurrent.SingleThreadEventExecutor$4.run(SingleThreadEventExecutor.java:989)
>  [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74) 
> [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at 
> io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
>  [netty-common-4.1.47.Final.jar:4.1.47.Final]
>       at java.lang.Thread.run(Thread.java:830) [?:?]
> [ERROR] 08:57:18.376 it.fox.Poller01.run() - Poller01 Exception
> java.util.concurrent.TimeoutException: null
>       at 
> java.util.concurrent.CompletableFuture.timedGet(CompletableFuture.java:1957) 
> ~[?:?]
>       at 
> java.util.concurrent.CompletableFuture.get(CompletableFuture.java:2092) ~[?:?]
>       at it.fox.Poller01.run(Poller01.java:24) [main/:?]
>       at java.lang.Thread.run(Thread.java:830) [?:?]
> [ERROR] 08:57:18.716 it.fox.Poller02.run() - Poller01 Exception
> java.util.concurrent.TimeoutException: null
>       at 
> java.util.concurrent.CompletableFuture.timedGet(CompletableFuture.java:1957) 
> ~[?:?]
>       at 
> java.util.concurrent.CompletableFuture.get(CompletableFuture.java:2092) ~[?:?]
>       at it.fox.Poller02.run(Poller02.java:24) [main/:?]
>       at java.lang.Thread.run(Thread.java:830) [?:?]
> [ERROR] 08:57:23.381 it.fox.Poller01.run() - Poller01 Exception
> java.util.concurrent.TimeoutException: null
>       at 
> java.util.concurrent.CompletableFuture.timedGet(CompletableFuture.java:1957) 
> ~[?:?]
>       at 
> java.util.concurrent.CompletableFuture.get(CompletableFuture.java:2092) ~[?:?]
>       at it.fox.Poller01.run(Poller01.java:24) [main/:?]
>       at java.lang.Thread.run(Thread.java:830) [?:?]
> [ERROR] 08:57:23.717 it.fox.Poller02.run() - Poller01 Exception
> java.util.concurrent.TimeoutException: null
>       at 
> java.util.concurrent.CompletableFuture.timedGet(CompletableFuture.java:1957) 
> ~[?:?]
>       at 
> java.util.concurrent.CompletableFuture.get(CompletableFuture.java:2092) ~[?:?]
>       at it.fox.Poller02.run(Poller02.java:24) [main/:?]
>       at java.lang.Thread.run(Thread.java:830) [?:?]
> ```
> I attach the corresponding pcap capture in order to help the debug.
> Regards,
> Stefano Bossi



--
This message was sent by Atlassian Jira
(v8.3.4#803005)

Reply via email to