https://issues.apache.org/jira/browse/PLC4X-246?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17188188#comment-17188188
 ] 

Sebastian Voss commented on PLC4X-246:
--------------------------------------

Hi Chris,

it seems to be something at the decoding level:
{code:java}
00:59:24.244 [nioEventLoopGroup-2-1] TRACE o.a.plc4x.java.spi.Plc4xNettyWrapper 
- Decoding 
TPKTPacket[payload=COTPPacketData[parameters={},payload=S7MessageResponse[tpduReference=10,parameter=<null>,payload=<null>,errorClass=129,errorCode=4],eot=true,tpduRef=0]]
00:59:24.245 [nioEventLoopGroup-2-1] TRACE o.a.plc4x.java.spi.Plc4xNettyWrapper 
- Checking handler HandlerRegistration#2 for Object of type TPKTPacket
00:59:24.245 [nioEventLoopGroup-2-1] TRACE o.a.plc4x.java.spi.Plc4xNettyWrapper 
- Handler HandlerRegistration#2 has right expected type TPKTPacket, checking 
condition
00:59:24.246 [nioEventLoopGroup-2-1] TRACE o.a.plc4x.java.spi.Plc4xNettyWrapper 
- Registration HandlerRegistration#2 does not match object TPKTPacket 
(currently wrapped to COTPPacketData)
00:59:24.246 [nioEventLoopGroup-2-1] TRACE o.a.plc4x.java.spi.Plc4xNettyWrapper 
- No registered handler found for message 
TPKTPacket[payload=COTPPacketData[parameters={},payload=S7MessageResponse[tpduReference=10,parameter=<null>,payload=<null>,errorClass=129,errorCode=4],eot=true,tpduRef=0]],
 using default decode method{code}

> S7 driver hangs on read
> -----------------------
>
>                 Key: PLC4X-246
>                 URL: https://issues.apache.org/jira/browse/PLC4X-246
>             Project: Apache PLC4X
>          Issue Type: Bug
>          Components: Driver-S7
>    Affects Versions: 0.7.0
>            Reporter: Sebastian Voss
>            Priority: Major
>         Attachments: s7_capture.pcapng
>
>
> I’m trying to read a value from an Siemens S7-1200 PLC). When I try to read a 
> value the read request is not being executed (I also do not receive an error 
> message or timeout).
> This is the simple program I created:
> {code:java}
> String url = "s7://172.29.118.20:102?controller-type=S7_1200";
> PlcDriverManager manager = new PlcDriverManager();
> PlcConnection connection = manager.getConnection(url);
> boolean isConnected = connection.isConnected();
> boolean canRead = connection.getMetadata().canRead();
> System.out.println(isConnected);  // prints true
> System.out.println(canRead);  // prints true
> String field = "%DB20:5.0:BOOL";
> PlcReadRequest request = connection
>           .readRequestBuilder()
>           .addItem("value-1", field)
>           .build();
> PlcReadResponse response = request.execute().get();  // here is hangs forever
> System.out.println(response.getFieldNames());
> connection.close();{code}
> I created a Wireshark capture and it seems the PLC is reporting:
> {code:java}
> [Error code: This service is not implemented on the module or a frame error 
> was reported (0x8104)]{code}
> Thanks to the help of [~cdutz] I figured out this is related to the 
> protection settings of the PLC. I will try to adjust those settings and 
> report back the result. Maybe the driver can be improved to report back those 
> error codes to the user.
>  
>    



--
This message was sent by Atlassian Jira