https://issues.apache.org/jira/browse/PLC4X-301?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17369420#comment-17369420
 ] 

Matthias Milan Strljic edited comment on PLC4X-301 at 6/25/21, 11:44 AM:
-------------------------------------------------------------------------

As Mentioned my solution would be to change the delimiter from ":" to ";" in 
the hope, that there will be no conflict because it is already a reserved 
character for the OPC UA namespace string. As [[email protected]] also 
already mentioned.


was (Author: nalim2):
As Mentioned my solution would be to change the delimiter from ":" to ";" in 
the hope, that there will be no conflict because it is already a reserved 
character for the OPC UA namespace string

> OPCUA address identifier with colon will not work
> -------------------------------------------------
>
>                 Key: PLC4X-301
>                 URL: https://issues.apache.org/jira/browse/PLC4X-301
>             Project: Apache PLC4X
>          Issue Type: Bug
>          Components: Driver-OPC-UA
>    Affects Versions: 0.8.0
>            Reporter: Torsten
>            Priority: Major
>
> If a field address has an identifier like 
> „ns=6;s=::AsGlobalPV:dsMES.Read.ProductionOrder“, the colons in the field 
> identifier does not match to the Regex in  
> org.apache.plc4x.java.opcua.protocol.OpcuaField.
> Such fields are not accesable at the moment.



--