The S7 will respond with:
* Error Class: 0x83
* Error Code: 0x04
if the user tries a write request and this is not explicitly enabled, we can
definitely handle this in a nicer way.
To fix the problem, you need to select the PLC in TIA, go into the
Properties dialog, select "Protection". You will probably notice there's an
Access Level Table, but you need to scroll down (even if it looks as if there
is nothing). There check the box in: "Permit access with PUT/GET communications
from remote partner...."
Would be cool if we could give our users a hint on this.