ottlukas opened a new issue, #599:
URL: https://github.com/apache/plc4x/issues/599

   The S7 will respond with:
    * Error Class: 0x83
    * Error Code: 0x04 
   
   if the user tries a write request and this is not explicitly enabled, we can 
definitely handle this in a nicer way.
   
   To fix the problem, you need to select the PLC in TIA, go into the 
Properties dialog, select "Protection". You will probably notice there's an 
Access Level Table, but you need to scroll down (even if it looks as if there 
is nothing). There check the box in: "Permit access with PUT/GET communications 
from remote partner...."
   
   Would be cool if we could give our users a hint on this.
   
   Imported from Jira 
[PLC4X-208](https://issues.apache.org/jira/browse/PLC4X-208). Original Jira may 
contain additional context.