https://issues.apache.org/jira/browse/PLC4X-208?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17630922#comment-17630922
 ] 

Lukas Ott commented on PLC4X-208:
---------------------------------

This issue has been migrated to https://github.com/apache/plc4x/issues/599

> [S7] When trying to write to a S7 device and writing is not explicitly 
> enabled, the PLC will respond with an error code
> -----------------------------------------------------------------------------------------------------------------------
>
>                 Key: PLC4X-208
>                 URL: https://issues.apache.org/jira/browse/PLC4X-208
>             Project: Apache PLC4X
>          Issue Type: Task
>          Components: Driver-S7
>    Affects Versions: 0.8.0
>            Reporter: Christofer Dutz
>            Assignee: Christofer Dutz
>            Priority: Major
>         Attachments: put-get-disabled.pcapng
>
>
> The S7 will respond with:
>  * Error Class: 0x83
>  * Error Code: 0x04 
> if the user tries a write request and this is not explicitly enabled, we can 
> definitely handle this in a nicer way.
> To fix the problem, you need to select the PLC in TIA, go into the Properties 
> dialog, select "Protection". You will probably notice there's an Access Level 
> Table, but you need to scroll down (even if it looks as if there is nothing). 
> There check the box in: "Permit access with PUT/GET communications from 
> remote partner...."
> Would be cool if we could give our users a hint on this.



--
This message was sent by Atlassian Jira
(v8.20.10#820010)

Reply via email to