SteinOv opened a new issue, #713: URL: https://github.com/apache/plc4x/issues/713
### What happened? In the Apache Camel integration the connection is established in the constructor of Plc4XEndpoint instead of the doStart() method in the Plc4XConsumer/Plc4XProducer. Although this is not explicitly mentioned in the documentation, this is required for features like [disabling auto-start](https://camel.apache.org/manual/configuring-route-startup-ordering-and-autostartup.html#_autostartup) or the [route controller](https://camel.apache.org/manual/route-controller.html) to work. If no connection can be made at startup, the constructor of the Plc4XEndpoint will throw an Exception and the program will crash immediately. So, to fix this, the connection should be established in the doStart() methods of the Plc4XConsumer/Plc4XProducer. ### Version v0.10.0 ### Programming Languages - [X] plc4j - [ ] plc4go - [ ] plc4c - [ ] plc4net ### Protocols - [ ] AB-Ethernet - [ ] ADS /AMS - [ ] BACnet/IP - [ ] CANopen - [ ] DeltaV - [ ] DF1 - [ ] EtherNet/IP - [ ] Firmata - [ ] KNXnet/IP - [ ] Modbus - [ ] OPC-UA - [ ] S7 -- This is an automated message from the Apache Git Service. To respond to the message, please log on to GitHub and use the URL above to go to the specific comment. To unsubscribe, e-mail: [email protected] For queries about this service, please contact Infrastructure at: [email protected]