   ### What happened?
   
   It seems that if the connection cache is used with low concurrency (The 
connection is returned to the pool without other threads waiting for it) a 
timer is started, that unfortunately never seems to be stopped. This results in 
more and more open threads accumulating until the first of the timers actually 
times out and canceles the connection.
   
   ### Version
   
   0.13.0-SNAPSHOT
   
   ### Programming Languages
   
   - [ ] plc4c
   - [ ] plc4go
   - [x] plc4j
   - [ ] plc4net
   - [ ] plc4py
   
   ### Protocols
   
   - [ ] AB-Ethernet
   - [ ] ADS /AMS
   - [ ] BACnet/IP
   - [ ] C-Bus
   - [ ] CANopen
   - [ ] EtherNet/IP
   - [ ] Firmata
   - [ ] IEC-69870
   - [ ] KNXnet/IP
   - [ ] Modbus
   - [ ] OPC-UA
   - [ ] Profinet
   - [ ] S7


-- 