   ### What happened?
   
   ## Description
   We are currently working on integrating a Rockwell PLC using the PLC4J 
library with the Ethernet/IP Protocol. While our implementation successfully 
communicates with a Rockwell CompactLogix PLC, we are encountering issues when 
attempting to connect to a Rockwell ControlLogix PLC.
   
   ## Observations
   During our analysis with Wireshark, we observed the following:
   
   - The initial `GetAttributesAll` call to the ControlLogix PLC fails, 
returning the error: 'General Status: Service not supported (0x08).'
   - In contrast, the same call works without issues on the CompactLogix PLC, 
where we receive responses with attributes for: 'Class: Message Router 
(0x0002)' and 'Class: Connection Manager (0x0006)'
   
   ## Current Understanding
   If the `GetAttributesAll` call fails, then the `useConnectionManager` and 
`useMessageRouter` boolean values are set to `false` in the `EipProtocolLogic` 
class. As a result, PLC4X is attempting to perform single requests.
   
   ### Issues Identified
   - Sending single requests sequentially is causing issues related to the 
PLC4X library.
   - Sending single requests when `useMessageRouter` and `useConnectionManager` 
are not active has also been problematic in the past in the PLC4X library, 
based on my understanding of the code. Therfore I would prefer the way via 
Message Router / Connection Manager.
   
   ## Idea
   - The `GetAttributeSingle` method may serve as a potential workaround 
instead of using GetAttributesAll, in order to get the attributes 'Class: 
Message Router (0x0002)' and 'Class: Connection Manager (0x0006)' one after the 
other. However, if the Message Router and Connection Manager are not 
functioning correctly, implementing this workaround may not solve the issue and 
we have also not tried to use GetAttributeSingle (just seen it in some 
documentation).
   
   ## Questions
   1. Does anyone know why the `GetAttributesAll` call may be failing with the 
ControlLogix PLC? 
   2. Any ideas on potential workarounds or solutions would be greatly 
appreciated.
   
   Thank you 
   
   
   ### Version
   
   v0.12.0
   
   ### Programming Languages
   
   - [ ] plc4c
   - [ ] plc4go
   - [x] plc4j
   - [ ] plc4net
   - [ ] plc4py
   
   ### Protocols
   
   - [ ] AB-Ethernet
   - [ ] ADS /AMS
   - [ ] BACnet/IP
   - [ ] C-Bus
   - [ ] CANopen
   - [x] EtherNet/IP
   - [ ] Firmata
   - [ ] IEC-69870
   - [ ] KNXnet/IP
   - [ ] Modbus
   - [ ] OPC-UA
   - [ ] Profinet
   - [ ] S7
   - [ ] S7-light


-- 
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.

To unsubscribe, e-mail: issues-unsubscr...@plc4x.apache.org.apache.org

For queries about this service, please contact Infrastructure at:
us...@infra.apache.org

Reply via email to