shekhartanwar commented on issue #2246:
URL: https://github.com/apache/plc4x/issues/2246#issuecomment-3268875769

   > Hi,
   > 
   > yeah ... well you "technically" close it after doing your thing, but it 
doesn't really close, it but return it to the cache (and potentially waiting 
threads). In your case I guess you have implemented part of the functionality. 
I just wanted to make sure that you don't expect the connection to be open 
indeffinitely. If you're checking things and potentially re-creating 
connections, you should be fine. But I guess your log output is simply the log 
of an operation failing and your code then creates a new connection the next 
time.
   
   Hello, I am seeing frequent connection resets with v0.13.1 s7-light driver. 
It reconnects within 1-2 seconds max, that's why i don't have a problem here, 
but i can't tolerate frequent connection resets.
   
   Please check the logs below.
   `
   2025-09-09T09:25:41.995+05:30 | 2025-09-09T03:55:41.993Z ERROR 1 --- 
[oopGroup-1424-1] o.a.p.j.s.c.DefaultNettyPlcConnection : unknown error, close 
the connection
   -- | --
     | 2025-09-09T09:25:41.995+05:30 | java.net.SocketException: Connection 
reset
     | 2025-09-09T09:25:41.995+05:30 | at 
java.base/sun.nio.ch.SocketChannelImpl.throwConnectionReset(Unknown Source) 
~[na:na]
     | 2025-09-09T09:25:41.995+05:30 | at 
java.base/sun.nio.ch.SocketChannelImpl.read(Unknown Source) ~[na:na]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.buffer.PooledByteBuf.setBytes(PooledByteBuf.java:255) 
~[netty-buffer-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.buffer.AbstractByteBuf.writeBytes(AbstractByteBuf.java:1132) 
~[netty-buffer-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.channel.socket.nio.NioSocketChannel.doReadBytes(NioSocketChannel.java:356)
 ~[netty-transport-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:151)
 ~[netty-transport-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:796) 
~[netty-transport-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:732)
 ~[netty-transport-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:658) 
~[netty-transport-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:562) 
~[netty-transport-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.util.concurrent.SingleThreadEventExecutor$4.run(SingleThreadEventExecutor.java:998)
 ~[netty-common-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74) 
~[netty-common-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
 ~[netty-common-4.1.123.Final.jar!/:4.1.123.Final]
     | 2025-09-09T09:25:41.995+05:30 | at 
java.base/java.lang.Thread.run(Unknown Source) ~[na:na]
     | 2025-09-09T09:25:41.996+05:30 | 2025-09-09T03:55:41.996Z INFO 1 --- 
[oopGroup-1424-1] o.a.p.j.s.c.NettyChannelFactory : Channel is closed, closing 
worker Group also
     | 2025-09-09T09:25:42.092+05:30 | 2025-09-09T03:55:42.092Z INFO 1 --- 
[ool-14-thread-1] c.v.p.service.impl.PlcS7Service : Creating PLC Connection...
   2025-09-09T09:25:42.092+05:30 | 2025-09-09T03:55:42.092Z INFO 1 --- 
[ool-14-thread-1] o.a.plc4x.java.DefaultPlcDriverManager : Instantiating new 
PLC Driver Manager with class loader null
   -- | --
     | 2025-09-09T09:25:42.092+05:30 | 2025-09-09T03:55:42.092Z INFO 1 --- 
[ool-14-thread-1] o.a.plc4x.java.DefaultPlcDriverManager : Registering 
available drivers...
     | 2025-09-09T09:25:42.092+05:30 | 2025-09-09T03:55:42.092Z ERROR 1 --- 
[ool-14-thread-1] c.v.p.service.impl.PlcS7Service : Plc connect error : Unable 
to find driver for protocol 's7-light'
     | 2025-09-09T09:25:42.092+05:30 | 2025-09-09T03:55:42.092Z ERROR 1 --- 
[ool-14-thread-1] c.v.p.watchdog.impl.WatchdogImpl : Exception occurred while 
initializing watchdog builder, Message : PLC connection is down
     | 2025-09-09T09:25:42.093+05:30 | 2025-09-09T03:55:42.092Z ERROR 1 --- 
[ool-14-thread-1] c.v.p.service.impl.PlcS7Service : Exception occurred while 
executing write request, Message
     | 2025-09-09T09:25:42.093+05:30 | java.lang.NullPointerException: null
     | 2025-09-09T09:25:42.168+05:30 | 2025-09-09T03:55:42.168Z INFO 1 --- 
[ool-10-thread-1] c.v.p.service.impl.PlcS7Service : Creating PLC Connection...
     | 2025-09-09T09:25:42.168+05:30 | 2025-09-09T03:55:42.168Z INFO 1 --- 
[ool-10-thread-1] o.a.plc4x.java.DefaultPlcDriverManager : Instantiating new 
PLC Driver Manager with class loader null
     | 2025-09-09T09:25:42.168+05:30 | 2025-09-09T03:55:42.168Z INFO 1 --- 
[ool-10-thread-1] o.a.plc4x.java.DefaultPlcDriverManager : Registering 
available drivers...
     | 2025-09-09T09:25:42.168+05:30 | 2025-09-09T03:55:42.168Z ERROR 1 --- 
[ool-10-thread-1] c.v.p.service.impl.PlcS7Service : Plc connect error : Unable 
to find driver for protocol 's7-light'
     | 2025-09-09T09:25:42.168+05:30 | 2025-09-09T03:55:42.168Z ERROR 1 --- 
[ool-10-thread-1] c.v.p.watchdog.impl.WatchdogImpl : Exception occurred while 
initializing watchdog builder, Message : PLC connection is down
   
   2025-09-09T09:25:42.655+05:30 | 2025-09-09T03:55:42.655Z INFO 1 --- [ 
scheduling-1] o.a.plc4x.java.DefaultPlcDriverManager : Registering available 
drivers...
   -- | --
     | 2025-09-09T09:25:42.657+05:30 | 2025-09-09T03:55:42.657Z INFO 1 --- [ 
scheduling-1] o.a.plc4x.java.DefaultPlcDriverManager : Registering driver for 
Protocol s7 (Siemens S7 (Basic))
     | 2025-09-09T09:25:42.657+05:30 | 2025-09-09T03:55:42.657Z INFO 1 --- [ 
scheduling-1] o.a.plc4x.java.DefaultPlcDriverManager : Registering driver for 
Protocol s7-light (Siemens S7 (Basic) (light))
   `
   
   I can see error like `Unable to find driver for protocol 's7-light'` but in 
multiple retries it's able to find the driver.
   I can also observe frequent connection resets throughout the day. This was 
not the case with 0.12.0 version. Is there anything else can i do here to 
improve the connection stability?


-- 