frankpuppa commented on issue #2229:
URL: https://github.com/apache/plc4x/issues/2229#issuecomment-3351777883

   Hello there, just to add a little note about this. In my case, ( I was using 
the PlcConnectionManager, not the CachedConnectionManager), the number of 
threads was increasing only between disconnections and reconnections, not 
between requests. 
   If you look at my PR #2241 I used the channel Inactive event which is fired 
when the device disconnects abruptly (unfortunately I could not test this on a 
real physical device and so I had to rely on the modbus simulator). In the 
handler, I propagate the event which closes the timer and shutdown the 
tm(RequestTransactionManager). Both these objects are responsible of the 
leakage, but the latter owns the plc4x-tm-threads, on shutdown it releases them.
    
   At the moment I have an application running 24/7 which polls roughly 20 
devices between S7(1200) and modbus and so far it is working fine. 
   Hope this helps.


-- 
This is an automated message from the Apache Git Service.