DvonHolten opened a new issue, #2388:
URL: https://github.com/apache/plc4x/issues/2388
### What happened?
when you add parameters to a S7 request, you have two ways to do it:
- `builder.addTagAddress( "name", "%DB69:68:STRING(20)" )`
- `builder.addTag( "name", S7Tag.of("%DB69:68:STRING(20)" )`
however, in the second form we get an error, because the `S7Tag.of()`
notation does not recognize the string-length parameter. Looking into
`S7Tag.of()` and `addTagAddress()` shows, that `S7Tag.of()` does not use the
regexes which could handle the added "(20)" length parameter. addTagAddress()
uses these regexes and can deal with this addresses.
### Version
V0.13.1
### Programming Languages
- [ ] plc4c
- [ ] plc4go
- [x] plc4j
- [ ] plc4net
- [ ] plc4py
### Protocols
- [ ] AB-Ethernet
- [ ] ADS /AMS
- [ ] BACnet/IP
- [ ] C-Bus
- [ ] CANopen
- [ ] EtherNet/IP
- [ ] Firmata
- [ ] IEC-69870
- [ ] KNXnet/IP
- [ ] Modbus
- [ ] OPC-UA
- [ ] Profinet
- [ ] S7
- [x] S7-light
--