Hi
Javier,
First, just a quick
note to let you know that upgrading to 0.8.2 has solved all of my APC UPS
graphing problems. Very handy to be able to do some historical tracking on
our UPS's.
So on to the next
item! I'm working on building a poller item that determines if a UPS
battery is good or bad. In the case of an APC, the OID is
.1.3.6.1.4.1.318.1.1.1.2.2.4.0. A return value of 1 indicates the
battery is ok and a return value of 2 indicates the battery needs to be
replaced. I've built a new poller item based on the included "a APC Output
Status" and it looks like this:
ID:
10001
Description: a APC
Battery Needs Replacing
Name:
replace_battery (if I'm reading the documentation right the name would only be
important if I wanted to create an RRD column to graph this
value)
Poller Command:
snmp_status
Parameters:
.1.3.6.1.4.1.318.1.1.1.2.2.4.0,1=OK Battery|2=Bad Battery
I've added the
poller item into the pre-existing APC Poller Group, and within the Poller Group
I've told the poller item to use the pre-existing Alarm APC backend (much like a
APC Output Status does). However, when I add a UPS host that has a known
bad battery, I don't get any alarm activity such as you would with the UPS
switching to battery or losing IP connectivity.
Any thoughts on what
I've missed?
Thanks,
Mike Concannon