On 6/11/2026 5:53 PM, Krzysztof Kozlowski wrote:
On 11/06/2026 13:12, Gaurav Kohli wrote:
Why? And where is this generic property defined? You cannot just
sprinkle generic properties in random bindings.
Ack, will add why part.
These names are matched with the thermal mitigation device identifiers
populated by remote firmware over QMI and define mitigation devices are
exposed as cooling devices.
No, -names correspond to values passed via DT, not some remote firmware.
The remote firmware should give you interface which is explicit and does
not need such properties.
thanks Krzysztof for review, We need tmd-names because of following reasons:
Following Daniel's series [1], the thermal framework supports
mapping multiple cooling devices per remoteproc/device via indexed
cooling-cells.
1) The thermal framework's cooling-maps reference
cooling devices by index (for #cooling-cells = <3>). Without tmd-names,
there's no way to know which index corresponds to which TMD, as firmware
may return tmd-names in any order.
below are the changes post new thermal mapping changes:
DT: tmd-names = "cdsp_sw", "xyz";
Firmware: ["cdsp_sw", "xyz1", "xyz2",]
Driver registers: Only "cdsp_sw" (index 0) and "xyz" (index 1)
This allows cooling-maps like below:
cooling-device = <&remoteproc 0 ...> // "cdsp_sw"
cooling-device = <&remoteproc 1 ...> // "xyz"
2) Not all firmware-provided TMDs should be
exposed as cooling devices. The tmd-names property acts as a filter,
allowing board-specific DT to select only the relevant TMDs for that
platform.
[1]
https://lore.kernel.org/all/[email protected]/
Without tmd-names in DT, it is unclear which index corresponds to which
binding. With #cooling-cells, tmd-names in DT provides an explicit
name-to-index mapping. Please suggest.
I don't get what is the index here. Index of what?
Best regards,