In addition, the manual emphasizes the desirability of having large and
short wires to the battery.  Size 0000 and less than 10 feet is recommended
for the 12 volt model..  They mention the need to accommodate high surge
currents.


Personally I have about 8 feet of 000.  I also have a three-phase, 100
A/leg, surface mount circuit breaker in that line.  It handles all loads we
use except if we use the microwave and then turn on the toaster oven.  Then
it will trip.  I guess it trips well below the rated inverter load of 2500
watts.


It may be helpful to cross-connect the battery bank.  That is, connecting
all terminals at the same voltage together.  So if you have 4 six-volt
batteries in series/parellel you would connect the two negatives in the
minus feed as well as the two positive terminals together, pretty much SOP,
but in addition one would also connect the two jumpers together that
connect each pair of batteries in series.  In theory this serves to help
keep the cells all working together better by reducing the effects of small
differences between cells.  If you had individual cells then all jumpers at
the same voltage level would be connected together.


Norm
S/V Bandersnatch
Lying Julington Creek
30 07.695N 081 38.484W


_______________________________________________
Liveaboard mailing list
[email protected]
To adjust your membership settings over the web 
http://www.liveaboardnow.org/mailman/listinfo/liveaboard
To subscribe send an email to [email protected]

To unsubscribe send an email to [email protected]
The archives are at http://www.liveaboardnow.org/pipermail/liveaboard/

To search the archives http://www.mail-archive.com/[email protected]

The Mailman Users Guide can be found here 
http://www.gnu.org/software/mailman/mailman-member/index.html

Reply via email to