hi, sorry to bother you again but your advice is very useful and helpful!

I have increased the reactive power at a bus and logged the data into Excel
spreadsheet (attached).  I was wondering if you could have a look at the voltage
collapse curve and comment on the authenticity of it -if it's realistic or not -
to me it seems to linear.

thanks so much,

shane.







Quoting David Vowles <[email protected]>:

> The following comment is not really about Matpower but rather wind farm 
> modelling.
> 
> A difficulty that can occur when modelling wind farms is that it is 
> common for the wind farm controllers to regulate the power factor at the 
> point of common coupling. Thus if, for example, the wind farm controls 
> the power factor to unity at the transmission system interface to the 
> wind farm there may be two levels of transformation between the 
> generator bus which represents the turbines in the wind farm and the HV 
> transmission system bus. Thus, it is necessary (in the case of DFIGs or 
> inverter connected turbines), to apriori estimate the reactive power 
> output of the turbines necessary for unity power factor at the point of 
> common coupling. In such cases it would be desirable for the loadflow 
> program to have facilities to allow a generator (or group of generators) 
> to regulate the power factor at a remote point.
> 
> Cheers,
> David.
> 
> Genevieve Coath wrote:
> > Hi,
> >
> > I have modelled wind farms in MATPOWER, and as Ray has suggested
> > below, did use negative values for the active power injection of the
> > wind farm (i.e. subtracted this from existing load at that bus), but a
> > positive value of reactive power consumption (i.e. added this to the
> > existing load Q demand at that bus) assuming that the wind farm
> > comprises asynchronous wind turbine generators. Shunt reactances or
> > susceptances can be entered as positive values in columns 5 and 6.
> >
> > Cheers,
> >
> > Genevieve
> >
> > On Mon, Mar 19, 2007 at 04:20:33PM -0400, Ray Zimmerman wrote:
> >   
> >> On Mar 19, 2007, at 4:07 PM, [email protected] wrote:
> >>
> >>     
> >>> Quoting Ray Zimmerman <[email protected]>:
> >>>
> >>>       
> >>>> On Mar 18, 2007, at 8:11 PM, [email protected] wrote:
> >>>>         
> >>>>> Wondering if it would be possible to model the integration of a
> >>>>> wind farm of say
> >>>>> 100MW using MATPOWER, thinking could enter the reactive power, is
> >>>>> this possible?
> >>>>>           
> >>>> If you are thinking of modeling it as a specified P and Q injection,
> >>>> you can include these in the bus matrix as negative loads.
> >>>>
> >>>>  Ray
> >>>>
> >>>>         
> >>> yes that was my initial plan. however is it possible to enter  
> >>> reactances and
> >>> susceptance for that option? excuse my ignorance in this area.
> >>>       
> >> I'm not sure I completely understand what you're trying to do,  
> >> but ... the constant power portion of a load is entered in cols 3 & 4  
> >> of the bus matrix, and the constant impedance portion in cols 5 & 6.  
> >> And yes, they can be combined.
> >>
> >> For a wind farm (or other source of power) it may make sense to use  
> >> negative values in cols 3 & 4, but since I'm not familiar with the  
> >> models I don't know what makes sense for columns 5 & 6, though I  
> >> assume if you're using them at all they should be positive.
> >>
> >> Sorry I'm not more familiar with the models for wind,
> >>
> >>    Ray
> >>     
> 
> 
> -- 
> David Vowles,
> Research Engineer,
> School of Electrical and Electronic Engineering,
> The University of Adelaide,
> Australia, 5005.
> 
> Phone: +61 8 8303 5416
> Fax:   +61 8 8303 4360
> 
> 