Dear Wu Jun,

I do not believe that the approach you propose will work because the
power-flow equations (normally) do not include the machine reactance. As
you know, when calculating the short-circuit impedance at a network
node, synchronous machines should be represented by a constant-voltage
behind an appropriate impedance. The appropriate impedance might
typically be the sub-transient reactance or transient reactance of the
machine, depending on the time-frame of interest. In the loadflow
computation, (typically) the generator terminal voltage is constant,
which represents the longer-term response of the machine due to the
action of the automatic voltage regulator (AVR).

Hope this helps,
David.

Wu Jun wrote:
> Ara and others,
>
> I think the short circuit currents (3-phase SC) can be easily calculated by 
> the practical formula shown as below, isn’t it? 
> Id=V(0)/Zdd
> where Id is the short circuit current (3-phase SC), V(0) is the initial 
> voltage at the failure point and Zdd is the self-reactance of the failure 
> point.
> So I think Matpower can also calculate it because all elements in the right 
> side of the formula can be achieved in the process of calculating the power 
> flow. But I am not familiar with the inner structure of Matpower. 
> I am wondering how to get the Zdd from it?
>
> --------------
> Yours sincerely,
> Wu Jun
> Unit:   State Key Lab. of Power Systems, 
>         Dep. of Electrical Engineering, 
>         Tsinghua University, P.R. China.
> Email:  [email protected]
> 2007-04-18
>
>
>
> 发件人: Panosyan, Ara
> 发送时间: 2007-04-13 20:21:58
> 收件人: [email protected]
> 抄送: 
> 主题: [?? Probable Spam] WG: Re: About the short circuit current
>
>
> Wu,
>
> as I wrote in my first email, I am not sure what each tool can, since I 
> haven't used any of them, but I thought maybe you would be interested in 
> knowing  about the available Matlab Tools for PS-Analysis.
>
> I am not sure what kind of analysis do you mean? Do you want to calculate 
> only the short circuit currents (3-phase SC)? Or the dynamic fault analysis? 
> I guess if it’s the 2nd one, then you should be able to use many tools. Short 
> circuit current calculation according to standard procedure (i.e. IEC 909 or 
> ANSI http://ieeexplore.ieee.org/iel1/28/5799/00222435.pdf?arnumber=222435) is 
> probably a bit trickier to program, because of its unsystematic nature. Maybe 
> that’s why most tools still don't have it.
>
> Regards
>
> Ara
>
>
> ------------------------------------
> Dipl.-Ing. Ara Panosyan
> University of Hannover
> Institute of Electric Power Systems
> [email protected]
> ------------------------------------
>
>
> -----Ursprüngliche Nachricht-----
> Von: [email protected] 
> [mailto:[email protected]] Im Auftrag von ??
> Gesendet: Freitag, 13. April 2007 10:44
> An: MATPOWER discussion forum
> Betreff: Re: [?? Probable Spam] Re: About the short circuit current
>
> Ara,
>
> Thanks for your attention and suggestion.
> I've read the paper and gotten more information about the PSAT from the 
> author's homepage. But unfortunately, the author said below words in one 
> presentation: The fault analysis and some other tools are still not available 
> as Matlab packages or toolboxes. So I have to go on looking for other tools. 
>
> --------------
> Yours sincerely,
> Wu Jun
> Unit:   State Key Lab. of Power Systems, 
>         Dep. of Electrical Engineering, 
>         Tsinghua University, P.R. China.
> Email:  [email protected]
> 2007-04-13
>
>
>
> 发件人: Panosyan, Ara
> 发送时间: 2007-04-12 21:09:08
> 收件人: MATPOWER discussion forum
> 抄送: 
> 主题: [?? Probable Spam] Re: About the short circuit current
>
> Wu,
>
> check this paper for some of the available Matlab based PS-Tools.
> But it doesn't look like any of them has the IEC-standard short-circuit 
> calculation (if that is what you are looking for?).
> I'm not sure thought, since I haven't used any of them.
>
> http://www.power.uwaterloo.ca/~claudio/courses/ece664/project/PSATpaper.pdf
>
> Ara
>
> ------------------------------------
> Dipl.-Ing. Ara Panosyan
> University of Hannover
> Institute of Electric Power Systems
> [email protected]
> ------------------------------------
>
>
> -----Urspr�ngliche Nachricht-----
> Von: [email protected] 
> [mailto:[email protected]] Im Auftrag von ??
> Gesendet: Donnerstag, 12. April 2007 14:31
> An: matpower-l
> Betreff: About the short circuit current
>
> Hi all,
>
> Can the Matpower calculate the short circuit currents?
> If it can not, which one can? Please introduce one toolbox in MATLAB for me.
> Thanks!
>
>
> --------------
> Yours sincerely,
> Wu Jun
> 2007-04-12
>   


-- 
David Vowles,
Research Engineer,
School of Electrical and Electronic Engineering,
The University of Adelaide,
Australia, 5005.

Phone: +61 8 8303 5416
Fax:   +61 8 8303 4360

<<attachment: dvowles.vcf>>

Reply via email to