I've sent it to you off-list.

   Ray

On Aug 7, 2008, at 5:36 AM, di wu wrote:

Thank you for your answer.

can you give me the paper about the deviation of DC power flow?
On Wed, Aug 6, 2008 at 9:17 PM, Ray Zimmerman <[email protected]> wrote:
Hi Di Wu,

I'm sorry for the delay in responding ... I had to find some time to give it a bit of thought.


On Jul 21, 2008, at 8:30 AM, [email protected] wrote:
I have two problem about the makeBdc function in Matpower.

1) Generally, in DC power flow, the tap settings of transformers are ignored. Why are the tap settings considered in building Bbus in Matpower?

I'm not sure what is generally done. The model used in MATPOWER is derived directly from the AC model with the following approximating assumptions:

- branch is lossless
- charging capacitance is negligible
- voltage magnitudes are ~ 1 p.u.
- angle differences across branches are small enough that the sin of the angle difference can be approximated by the angle itself.

I might be able to pull the derivation from a paper I'm preparing if you need to see the details.


2) If the tap settings can't be neglected, can I modify the Bbus as follows?


%% for each branch, compute the elements of the branch B matrix and the phase
%% shift "quiescent" injections, where
%%
%% | Pf | | Bff Bft | | Vaf | | Pfinj |
%% | | = | | * | | + | |
%% | Pt | | Btf Btt | | Vat | | Ptinj |
%%
stat = branch(:, BR_STATUS); %% ones at in-service branches
b = stat ./ branch(:, BR_X); %% series susceptance
tap = ones(nl, 1); %% default tap ratio = 1
i = find(branch(:, TAP)); %% indices of non-zero tap ratios
tap(i) = branch(i, TAP); %% assign non-zero tap ratios

/************** modified codes **********************/
Btt = b;
Bff = b ./ (tap .*tap);
Bft = - b ./ tap;
Btf = - b ./ tap;

%% build Bbus
f = branch(:, F_BUS); %% list of "from" buses
t = branch(:, T_BUS); %% list of "to" buses
Cf = sparse(f, 1:nl, ones(nl, 1), nb, nl); %% connection matrix for line & from buses Ct = sparse(t, 1:nl, ones(nl, 1), nb, nl); %% connection matrix for line & to buses Bbus = Cf * spdiags(Bff, 0, nl, nl) * Cf' + ... %% Bff term of branch admittance Cf * spdiags(Bft, 0, nl, nl) * Ct' + ... %% Bft term of branch admittance Ct * spdiags(Btf, 0, nl, nl) * Cf' + ... %% Btf term of branch admittance
Ct * spdiags(Btt, 0, nl, nl) * Ct'; %% Btt term of branch admittance

I don't think this is correct. For a non-phase shift transformer, it results in Pt = -tap * Pf. The tap ratio relates the voltages and currents on the primary and secondary sides of an ideal transformer, but the power flow should be equal.

--
Ray Zimmerman
Senior Research Associate
428-B Phillips Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645





--
Di Wu
POLITECNICO DI TORINO
Dipartimento di Ingegneria Elettrica
Corso Duca degli Abruzzi, 24,
10129 TORINO - ITALY
Tel . +39 011 090 7117