Because I want to have PF=0.9 or 0.95 for all generators. As you know, it is
very important

On Mon, Mar 14, 2011 at 16:36, Ray Zimmerman <[email protected]> wrote:

> You need a row of A for each generator, each one with QPratio in the column
> corresponding to Pg(i) and -1 in the column corresponding to Qg(i) ...
>
> mpc.A = sparse([1:ng; 1:ng], [2*nb+(1:ng); 2*nb+ng+(1:ng)],
> [QPratio*ones(ng,1); -ones(ng,1)], 1:ng, 2*nb+2*ng);
>
> As I said, this is likely to make the OPF infeasible, so I'm not sure why
> you'd want to do it.
>
>  --
> Ray Zimmerman
> Senior Research Associate
> 211 Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
>
>
>
>
> On Mar 14, 2011, at 11:17 AM, Roberto Carvalini wrote:
>
> Thank you very much.
>
> Is it possible for you to give an example, for example case9, for all
> generators? I will be appreciate if you do it.
>
> Best Regards
>
> R. Carvalini
>
> On Mon, Mar 14, 2011 at 16:08, Ray Zimmerman <[email protected]> wrote:
>
>> The *A* matrix is from equation (5.25) in the User's 
>> Manual<http://www.pserc.cornell.edu/matpower/manual.pdf>.
>> As I mentioned, the coefficients need to go in the columns corresponding to
>> Pg(1) and Qg(1). So, Pg(1) is in the first column following the voltage
>> angles (1st nb columns) and magnitudes (next nb columns), so it's in column
>> 2*nb+1. For Qg(1) it's the first column after the Pg columns, so 2*nb (for
>> the voltage angles and magnitudes) plus ng columns for Pg.
>>
>> Yes, if you wanted to do this for all generators, you need to include a
>> row in *A* for each. Be careful though, this will likely over-constrain
>> the problem and make it infeasible. If all generators have a fixed power
>> factor, then balancing the real power output to match the load will mean a
>> specific reactive power output as well, which will not necessarily match the
>> reactive power load.
>>
>> --
>>  Ray Zimmerman
>> Senior Research Associate
>> 211 Warren Hall, Cornell University, Ithaca, NY 14853
>> phone: <%28607%29%20255-9645>(607) 255-9645
>>
>>
>>
>> On Mar 11, 2011, at 11:40 AM, Roberto Carvalini wrote:
>>
>> Thank you very much.
>>
>> I have read the manual but I didn't understand by which formula you
>> computed this matrix (highlighted)
>>
>> mpc.A = sparse([1; 1], *[2*nb+1; 2*nb+ng+1]*, [QPratio; -1], 1,
>> 2*nb+2*ng);
>>
>>  and if want to define the same PF for all generators, must I repeat this
>> for all or it depends on the type buses (PV or Slack)?
>>
>> Regards
>>
>> R. Carvalini
>>
>> On Fri, Mar 11, 2011 at 16:27, Ray Zimmerman <[email protected]> wrote:
>>
>>> Dirk's suggestion is fine for a simple power flow. But if you want to run
>>> an OPF, where the generator dispatch is to be determined by the
>>> optimization, but subject to a constant power factor constraint, then you
>>> will need to supply an additional user-defined linear constraint. For
>>> example, if you want to run case9 with a constant power factor constraint of
>>> 0.95 on the first generator, you could do it like this ...
>>>
>>> define_constants;
>>> mpc = loadcase('case9');
>>> nb = size(mpc.bus, 1);
>>> ng = size(mpc.gen, 1);
>>> pf = 0.95;
>>> QPratio = sqrt(1/pf^2 -1);
>>> %% add constraint that QPratio * Pg(1) - Qg(1) = 0
>>> mpc.A = sparse([1; 1], [2*nb+1; 2*nb+ng+1], [QPratio; -1], 1, 2*nb+2*ng);
>>> mpc.l = 0;
>>> mpc.u = 0;
>>> r = runopf(mpc);
>>> resulting_pf = r.gen(1, PG) / sqrt(r.gen(1, PG)^2 + r.gen(1, QG)^2)
>>>
>>> The important part here is defining the A matrix properly, where the
>>> columns correspond to voltage angles, voltage magnitudes, generator real
>>> injections, and generator reactive injections (2*nb + 2*ng columns in all).
>>> So the coefficients for our constraint co in the columns corresponding to
>>> Pg(1) and Qg(1).
>>>
>>>  --
>>> Ray Zimmerman
>>> Senior Research Associate
>>> 211 Warren Hall, Cornell University, Ithaca, NY 14853
>>> phone: <%28607%29%20255-9645> <%28607%29%20255-9645>(607) 255-9645
>>>
>>>
>>>
>>> On Mar 11, 2011, at 9:50 AM, Dirk Van Hertem wrote:
>>>
>>>  You model your generator as a load, so it is not represented in your gen
>>> matrix. Of course, if you want model your generator in a unit commitment,
>>> this may not be trivial...
>>>
>>> Dirk
>>>
>>> On 03/11/2011 12:32 PM, Roberto Carvalini wrote:
>>>
>>> Thank you
>>>
>>> How can I add? my problem is this
>>>
>>> Best Wishes
>>>
>>>  Roberto
>>>
>>>
>>> On Fri, Mar 11, 2011 at 12:22, Dirk Van Hertem 
>>> <[email protected]>wrote:
>>>
>>>> You can just define them as a PQ bus with negative power... (negative
>>>> load)
>>>>
>>>> Dirk
>>>>
>>>>
>>>> On 03/11/2011 12:11 PM, Roberto Carvalini wrote:
>>>>
>>>>> Hi
>>>>>
>>>>> How can I define constant power factor in MAPOWER for example, for
>>>>> generators PF=0.9?
>>>>>
>>>>> Please help me
>>>>>
>>>>> Regards
>>>>>
>>>>> Roberto
>>>>>
>>>>>
>>>>>
>>>>
>>>>  --
>>>> Dirk Van Hertem                       [email protected]
>>>> Electrical Engineering Department  http://www.esat.kuleuven.be/electa
>>>> K.U. Leuven, ESAT-ELECTA                     GSM: +32-(O)498-61.74.98
>>>> 10, Kasteelpark Arenberg, B-3001 Heverlee        fax:
>>>> <%2B32-16-32.19.85> <%2B32-16-32.19.85> <%2B32-16-32.19.85>
>>>> +32-16-32.19.85
>>>>
>>>>
>>>>
>>>
>>>
>>> --
>>> Dirk Van Hertem                       [email protected]
>>> Electrical Engineering Department  http://www.esat.kuleuven.be/electa
>>> K.U. Leuven, ESAT-ELECTA                     GSM: +32-(O)498-61.74.98
>>> 10, Kasteelpark Arenberg, B-3001 Heverlee        fax:  <%2B32-16-32.19.85> 
>>> <%2B32-16-32.19.85>+32-16-32.19.85
>>>
>>>
>>>
>>>
>>
>>
>>
>>
>
>
>
>
>


Best Wishes

Roberto

Reply via email to