Ray,
Since voltage magnitude is assumed to be 1.0pu in dc power flow and so GSF,
does it make sense to factor in off-norminal transformer taps  in gsf
calculation?
Cuong

On Sep 26, 2011 9:41 AM, "Ray Zimmerman" <[email protected]> wrote:
> Or ...
>
> 3. You can call the makePTDF function which will compute the shift factors
for you directly (see section 4.4 in the manual). It essentially does what
you suggest in number 1, but using makeBdc (which does not ignore tap)
rather than makeB.
>
> --
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
>
>
>
>
> On Sep 25, 2011, at 9:22 PM, Cuong P Nguyen wrote:
>
>> Ray,
>>
>> I understand there are two ways of calculating generation shift factor,
>>
>> 1. From makeB function, one could calculate the B prime matrix( Bp), then
one can remove the row/column associated with the reference bus. THE
TRANSFORMER TAP IS IGNORED while Bp is formed. Therefore, we can compute the
flow on the lines by injecting 1 MW at a bus i by Bp\dP where dP(i)=1 only
at bus i, zeros everywhere else, this flow is called generation shift
factor.
>>
>> 2. We repeat the procedure above by setting 1MW injection at bus i, the
injection at all other buses set to 0. Then call rundcpf, we could end up
with the line flow which we is essentially generation shift factor. But the
RUNDCPF DOES CONSIDER TAP.
>>
>> Which one is correct in calculating generation shift factor?
>>
>> Thanks
>> Cuong
>

Reply via email to