Dear Shri,
Thank you for your reply.Yes I managed to do that by multiplying all the
loads by 3 and running PF (Power Flow).
The thing is that if you multiply all the loads by 3 you will get the
gerenartion at the slack bus equal to 454.7 MW.
If loads are multiplied by 3.5 then power gerenartion at the bus 1 will be
615 MW .
My questions are :
1-Isn't any limit for slack(swing) bus that it goes up by increasing the
load?
2-If theresn't any limit why increasing loads cannot make up for voltage
drop at some buses?
Regards
Iman

On Wed, Jun 13, 2012 at 8:43 PM, Shri <[email protected]> wrote:

>
> On Jun 13, 2012, at 10:41 AM, iman wrote:
>
> > Dear all,
> >
> > Has anyone managed to see voltage drop in MATPOWER(for example below 0.9
> pu)?
> Yes, absolutely.
> If you scale the loads high enough you should see a drop in the voltages
> below the threshold you want. (unless you are (a) running a power flow and
> scaling the swing bus load only ;)  or (b) running an OPF with Vmin = 0.9
> pu )
>
> > The fact is in real bus systems when you increase loads, you experience
> voltage drop at some points but with matpower you can't see that.In real
> life substation's output (transformer MVA) and lines are limited but in
> MATPOWER the more you raise loads, the more power comes from substation!
> > Has anyone have an idea?
> > --
> >
> > Iman
> >
>
>
>
>


-- 
Best regards
Iman