hi Iman,
thank you so much for your quick response. I still have some questions
which I want to post:
so just as an example (values are taken from case9):
mpc.baseMVA = 100;
voltage of reference bus (or which voltage do i have to take?): 345kV
-> Z_base = 119.0250
my branch is
"4 5 0.017 0.092 0.158 250 250 250 0 0 1
-360 360;"
so i take
Z_pu = 0.017 + 0.092i
Z_pu * Z_base = 2.0234 +10.9503i
So R = 2.0234 and X = 10.9503?
For b I dont know what to do because there's no Q in the branch matrix,
online in the bus-matrix?
thank you in advance,
laurin
Am 17.08.2012 14:36, schrieb iman:
Dear Laurin
First calculate the impedance for R and X.You will have Z p.u
=R+JX.Then multiply it by Z base which is calculated by Z base=V^2/S
in which V and S are the base voltage and apparent power of the system
respectively.In the end multiply Z p.u by Z base to get the actual value.
In per Unit system Q injected to buses is the same as susceptance .So
Bs p.u=Q inj P.u. Simply multiply it to S base to get the actual Q
injected.
Hope that it is understandable
Regards
Iman
On Fri, Aug 17, 2012 at 1:21 PM, Laurin Vierrath <[email protected]
<mailto:[email protected]>> wrote:
hi there,
in mpc.branch there are columns defining r, x and b. those values
are "per unit". what do i have to do or how do i have to calculate
to get the actual value of r, x and b?
thank you!
laurin
--
Best regards
Iman