Yes, although the default value of 0 (meaning no tap switching capability)
actually means a 1.0 tap, that is, a nominal ratio.

carlos.

On Wed, Aug 29, 2012 at 2:26 PM, Cansu Yildirim <[email protected]> wrote:
> Thank you very much for your quick answer Carlos!
>
> So in my case, since I have just a normal transformer, this would mean that 
> the tap parameter is zero right?
>
> Regards,
>
> Cansu
>
>
>
> On 29.08.2012, at 19:57, "Carlos Murillo" <[email protected]> wrote:
>
>> Matpower uses the one line network representation in the  per unit
>> system. One of the main ideas behind the per unit system is to get rid
>> of all the transformers and instead represent all voltages normalized
>> to the nominal voltage of the branch/bus in question.  Variable tap
>> transformers are special transformers that can be tapped at points off
>> the nominal ratio. That is what the tap parameter represents; it does
>> not represent the turns ratio of the transformer.  Please refer to any
>> textbook on power systems to see how the per unit system is employed.
>>
>> carlos.
>>
>> On Wed, Aug 29, 2012 at 1:09 PM, Cansu Yildirim <[email protected]> 
>> wrote:
>>> Hello,
>>>
>>> I'm currently trying to get familiar with matpower. I have following problem
>>> with the 'transformer off nominal ratio'.
>>>
>>> I need to model a transformer. The values given are following one:
>>>
>>> U1:                                 20 kV
>>> U2:                                 0.4 kV
>>> rated power:                400 kVA
>>> no load losses:             0.61
>>> no load current (%):    0.1525
>>> u_k:                                3.85
>>> Cu losses:                      4.6 kW
>>> switching group:          Dy5
>>>
>>> I have following questions:
>>>
>>> 1) how do I calculate the TAP? When I look into the casefiles, I can see
>>> that the value fpr the tap is most time between 0.8 and 1.5
>>>     I would have calculated by dividing 20kV/0.4KV=25 which does not seem
>>> to be the correct value for the tap.
>>>
>>> 2) How do I identify the BR_X and BR_B ? When I look into the equivalent
>>> circuit diagram I know that there are more components that need to be
>>> calculated. So what
>>>    do these parameters mean for the transformer?
>>>
>>> I would be grateful for any help.
>>>
>>>
>>> Kind regards,
>>>
>>>
>>> Cansu Yildirim
>>>
>>>
>>
>
>

Reply via email to