Iman,

First of all, you should get exactly the same maximum lambda when you vary the 
load at a specific bus, because the lambda is relative to system MVA base (ie, 
baseMVA). I just did some testing in the way you mentioned and the results did 
come out exactly the same. 

The reason you got different and higher maximum lambda is probably related to 
the way you changed load. If you only double the active power of a load and 
kept the reactive power as it was, the power factor would be much higher. And 
you will likely see higher loadability, ie, maximum lambda.

Please note that, in the CPF program, both active and reactive power at the 
specified bus will be varied in order to keep the initial power factor as 
implied in the case file. Also note that load variations at multiple buses are 
currently not supported, and I have been evaluating approaches of implementing 
that piece.

If you have any other specific needs regarding CPF enhancement, please feel 
free to contact me off-list.

Rui (Ray) Bo, Ph.D, SMIEEE

Regulatory and Economic Studies Department

Midwest ISO

1125 Energy Park Drive

St.Paul, MN 55108

Phone: (651) 632-8447

Email: [email protected], [email protected]



From: iman 
Sent: Monday, October 08, 2012 05:54
To: MATPOWER discussion forum 
Subject: CPF

Dear all,
I have done CPF for IEEE 30 case and got lamda max as 1.26 .Then I doubled all 
loads and got lamda max as 3.17.How that is possible?Am I be doing something 
wrong?
Since generators are kept constant logically by doubling all loads, maximum 
loadability (lamda max) should decrease.Shouldn't it?
Thanks
Iman