For finding the LMPs of remaining load buses, you require utility function of 
the load buses. values of some utility functions are given in the following 
paper. 
H Liu et al., "Social welfare maximization in transmission enhancement 
considering network congestion", IEEE trans. on power systems, vol. 23, no. 3, 
August 2008, pp. 1105-1114. Please refer table no. VII on page no. 1113.


________________________________
 From: Khirad Dhabhar <[email protected]>
To: MATPOWER discussion forum <[email protected]> 
Sent: Monday, 4 March 2013 4:05 PM
Subject: Re: performing lmp calculation
 

Mr Karthik.
 
Let me take the 30 bus case as an example. Thus their are 6 gen and hence 6 
cost functions.Thus when i take the partial differential i will get six 
equations. Thus the LMP values of the generator bus. I want the LMP values of 
all the 30 buses. How do we get that.

Thanks 
khirad
  


On 2 March 2013 11:24, Kartik Pandya <[email protected]> wrote:

If your problem size is small then  you should get same opf results with ABC 
method and MINOS (MATPOWER) solver. but for large scale problem,
>to get LMP with ABC, first run opf with ABC to get Pg of all generators. then 
>get first order partial derivatives of the quadratic cost functions of all 
>generators with respect to pg. then in the obtained equations substitute 
>Optimal values of pg to obtain LMPs. 
>---
>
>
>
>________________________________
> From: Ray Zimmerman <[email protected]>
>To: MATPOWER discussion forum <[email protected]> 
>Sent: Thursday, 28 February 2013 9:14 PM
>Subject: Re: performing lmp calculation
> 
>
>
>If your OPF solution matches MATPOWER's OPF solution, then you can simply use 
>the LMP values computed by MATPOWER's OPF, found in results.bus(:, LAM_P). If 
>your solution does not match, then I'm afraid it's up to you to demonstrate 
>that it is even a solution to the OPF problem, i.e. that the optimality 
>conditions are satisfied. Not sure how MATPOWER can help you here.
>
>
>-- 
>Ray Zimmerman
>Senior Research Associate
>419A Warren Hall, Cornell University, Ithaca, NY 14853
>phone: (607) 255-9645
>
>
>
>
>On Feb 28, 2013, at 4:00 AM, Khirad Dhabhar <[email protected]> wrote:
>
>Hi guys. I am doing my mtech project. Now i have been able to successfully 
>create an ABC(artificial bee colony) based algorithm to solve the optimal 
>power flow. Now i require the LMP (lambda values) for my solution. How can i 
>use mathpower to use my opf results to calculate the LMP values. 
>>
>>Thank  you 
>>
>>khirad
>>
>>
>>-- 
>>Friendship is like a red rose with a green stem
>>
>
>
>


-- 
Friendship is like a red rose with a green stem

Reply via email to