Table B-3 in the User's Manual (or help caseformat) describes the fields of the 
branch matrix. RATE_A is the limit used by runopf(). Please note that for an AC 
power flow model it is an MVA limit, and for DC power flow it is a MW limit. So 
that saturation percentage as you call it would be …

define_constants;
if <AC power flow>
  saturation = sqrt(results.branch(:, PF).^2 + results.branch(:, PT).^2) ./ 
results.branch(:, RATE_A);
else
  saturation = abs(results.branch(:, PF)) ./ results.branch(:, RATE_A);
end

I'm afraid I don't understand your 3rd question.

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Apr 3, 2013, at 1:18 AM, Yahook K <[email protected]> wrote:

> Respected Sir,
> 
> From mpc.branch, I can get the From bus injection and the To bus injection of 
> each branch. But how can I calculate the saturation percentage of the branch? 
> For example, the branch has a limit of 15 MW, and there are 5 MW flowing in 
> this branch. I think to calculate the saturation percentage we do 5/15=1/3
> 
> Another question is where to find the limit for each branch?
> 
> The third question would be if I wanna set the branch saturation percentage 
> to 50%, 90% 120%, break. How can I do it? Can you give me some guidance?
> 
> Please shed light on me. Thank you.
> 
> 

Reply via email to