Thanks for the feedback,
 
I already tried this idea and compared with the results obtained from
another simulation software. Actually the results from Matpower in this
case are slightly deviated in terms of losses and voltages.
 
I'm not sure if there is another way to get more accurate results.
 
Thanks,
 
Basem Idlbi
Division Systems Engineering and Distribution Grids
Fraunhofer Institute for Wind Energy and Energy System Technology,
IWES
Königstor 59 | 34119 Kassel / Germany
Phone +49 561 7294-166 | Fax +49 561 7294-200
 
>>> Carlos E Murillo-Sanchez <[email protected]> 4/16/2013
3:21 >>>
The standard branch model in matpower does not include the shunt
conductance gc and susceptance bm that are normally used to model the
iron loss current and magnetizing current, respectively, in a
transformer.  However, you could use a shunt conductance and a shunt
susceptance (specified respectively in MW and in this case negative MVA
at nominal V, type help idx_bus for details) at the corresponding "from"
bus in the bus table to represent these.  It would not be exactly like
the standard "T" transformer model with the primary and secondary
leakage reactances + winding resistances in the branches and the
magnetizing and loss currents flowing down the center in the stem of the
"T"; rather, the shunt elements would be right at the "1" port
connections followed by the series r and x specified in the branch
matrix. The shunt elements could actually be located also at the "to"
bus instead; I guess that if the primary leakage reactance is higher
than the secondary's I would put the shunt elements at the secondary's
bus and viceversa.

carlos.

Basem Idlbi wrote:


Hi all,
 
I'm trying to calculate the transformer losses including the iron
losses.
The available parameters are the resistance in [pu], reactance in [pu],
no load losses in [W] and no load current in [%].
 
Do you know how to represent the transformer in Matpower for this case,
and how to calculate the losses?
 
Thanks in advance for any feedback,
 
 
Basem Idlbi
Division Systems Engineering and Distribution Grids
Fraunhofer Institute for Wind Energy and Energy System Technology,
IWES
Königstor 59 | 34119 Kassel / Germany
Phone +49 561 7294-166 | Fax +49 561 7294-200
 

Reply via email to