1) Make sure that when you isolate a bus you set it's BUS_TYPE to NONE and that 
your system still has a REF bus.
2) I'm not sure what you mean, but you can always load the case and make 
changes before running it, like …

define_constants;
mpc = loadcase('case118');
mpc.branch(110, BR_STATUS) = 0;
r = runopf(mpc);

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Apr 20, 2013, at 10:53 PM, Ashwin Venkataramanan <[email protected]> wrote:

> Dear Dr.Zimmerman
> 
>                I am a graduate student in electrical engineering from Arizona 
> state university. I have a doubt about opening buses using MATPOWER. I have 
> two questions.
> 
> 1)     My simulation involves removing a substation out of the network and 
> testing if the power flow converges. Just like first contingency analysis for 
> substations. Each bus is characterized as a substation or in some cases 
> combination of 2 buses are classified as substation. I have read the MATPOWER 
> user manual, from which I find only ways to remove branches and generator 
> from the network. I have tried the simulation by removing the branches 
> connected to the bus using the command
> 
>                    mpc.branch(110,BR_STATUS)=0;
> 
> for removing the branch 110 which may connect two buses. Similarly removing 
> all the branches connected to a bus in order to isolate a bus. I believe this 
> approach is right to remove a bus. But my powerflow diverges each time I 
> remove any bus(or substation). I believe this will not be a case as system 
> most of time must work for first contingency involving substation. I have 
> tested my code on both 118 and 30 bus case. Is there any way to remove bus 
> directly off other than removing using the branches(above mentioned approach) 
> ?
> 
>  2)  Is there any way to do convert the existing “case118.m” to modified 118 
> bus?
> 
> 
> Best Regards
> 
> Ashwin Venkataramanan
> 
> Arizona state university
> 

Reply via email to